On an eicr we can write LIM for L-N testing and do a test with L-N connected to earth if there's too many electronics to unplug.

What about on an EIC when only doing something like a CU upgrade? Can't do the IR test between L-N with too many things to unplug and we can't write LIM on EIC in the live-live column?

So what to write in the L-L test columns on an EIC?

I know its always good to do the EICR before upgrade, but still got to do the EIC afterwards.

Thanks in advance.
 
According to BS7671 an EIC should detail the extent of the work it covers and should include schedules of inspections and test results detailing appropriate inspections and tests which relate to the work covered by the certificate.
Further an EIC should not be used to report on the condition of an existing installation.
As such you are not required to include the results of inspecting and testing existing circuits in the schedules.
Some may argue that you are in fact prohibited from doing so.

If you are unable to conduct an unneccessary test, then it is not a limitation, so does not need to be recorded as such.
 
According to BS7671 an EIC should detail the extent of the work it covers and should include schedules of inspections and test results detailing appropriate inspections and tests which relate to the work covered by the certificate.
Further an EIC should not be used to report on the condition of an existing installation.
As such you are not required to include the results of inspecting and testing existing circuits in the schedules.
Some may argue that you are in fact prohibited from doing so.

If you are unable to conduct an unneccessary test, then it is not a limitation, so does not need to be recorded as such.

So we leave the columns blank then? Surely we can't just leave them blank or write NA?

I'm just trying to know what's the best way to fill the form, I know what tests to do and how to do them.
 
So we leave the columns blank then? Surely we can't just leave them blank or write NA?

I'm just trying to know what's the best way to fill the form, I know what tests to do and how to do them.
You haven't conducted the test, so "N/A" would be fair enough in my opinion. And in the section of the certificate asking about limitations on the inspection and testing obviously I would note that insulation testing has not been carried out between live conductors due to the presence of connected lamps and loads.

Live conductors to Earth is the most important one for insulation testing anyway - in fact in many countries the requirement is simply for insulation testing to Earth.
 

Reply to IR testing on CU upgrade in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top