Hi All ,
When testing insulation resistance on a domestic lighting circuit do you just join live/neutral and test down to earth otherwise if your testing live to neutral presumably you have to close all switches and remove all the lamps in the circuit.

Thanks Chris
 
Des 56 , yep , i'm aware of that but i was wondering how you would do IR test on a lighting circuit if asked to do so on the actual part 'p' assesment ? :)

Regards
Chris
 
An insulation resistance test is done over the whole of the installation
It needs to be done on individual circuits only when a problem may exist

And if it is done on circuits individually then calculations would need to be done to ensure that the installation is satisfactory, i.e. 1/Rt = 1/R1 + 1/R2 etc.

The values in BS7671 relate to the installation/dis. board - not to individual circuits!
 
And if it is done on circuits individually then calculations would need to be done to ensure that the installation is satisfactory, i.e. 1/Rt = 1/R1 + 1/R2 etc.

The values in BS7671 relate to the installation/dis. board - not to individual circuits!


Are you saying that if you IR tested six circuits individually, and they each gave a reading of 5 M ohms, the installation wouldn't comply, and you would fail it.:D
 
Are you saying that if you IR tested six circuits individually, and they each gave a reading of 5 M ohms, the installation wouldn't comply, and you would fail it.:D

If below 2 Megohms then you would need further investigation, i.e. checking individual circuits. You already have the values for the individual circuits.

The point I was making was that the insulation resistance value is not just fo the circuit (read the Regulation carefully).
 
If below 2 Megohms then you would need further investigation, i.e. checking individual circuits. You already have the values for the individual circuits.

The point I was making was that the insulation resistance value is not just fo the circuit (read the Regulation carefully).

I know, I'm just causing trouble - that's why the big cheesy grin:D

It's an interesting scenario, though, 'cause it gives an overall resistance of 0.83 Mohms for the installation, yet each individual circuit complies.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
IR Testing on domestic installations.
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
electek,
Last reply from
WayneL,
Replies
22
Views
5,607

Advert

TrueNAS JBOD Storage Server

Back
Top