electek

Hi All ,
When testing insulation resistance on a domestic lighting circuit do you just join live/neutral and test down to earth otherwise if your testing live to neutral presumably you have to close all switches and remove all the lamps in the circuit.

Thanks Chris
 
An insulation resistance test is done over the whole of the installation
It needs to be done on individual circuits only when a problem may exist

And if it is done on circuits individually then calculations would need to be done to ensure that the installation is satisfactory, i.e. 1/Rt = 1/R1 + 1/R2 etc.

The values in BS7671 relate to the installation/dis. board - not to individual circuits!
 
And if it is done on circuits individually then calculations would need to be done to ensure that the installation is satisfactory, i.e. 1/Rt = 1/R1 + 1/R2 etc.

The values in BS7671 relate to the installation/dis. board - not to individual circuits!


Are you saying that if you IR tested six circuits individually, and they each gave a reading of 5 M ohms, the installation wouldn't comply, and you would fail it.:D
 
Are you saying that if you IR tested six circuits individually, and they each gave a reading of 5 M ohms, the installation wouldn't comply, and you would fail it.:D

If below 2 Megohms then you would need further investigation, i.e. checking individual circuits. You already have the values for the individual circuits.

The point I was making was that the insulation resistance value is not just fo the circuit (read the Regulation carefully).
 
If below 2 Megohms then you would need further investigation, i.e. checking individual circuits. You already have the values for the individual circuits.

The point I was making was that the insulation resistance value is not just fo the circuit (read the Regulation carefully).

I know, I'm just causing trouble - that's why the big cheesy grin:D

It's an interesting scenario, though, 'cause it gives an overall resistance of 0.83 Mohms for the installation, yet each individual circuit complies.
 

Reply to IR Testing on domestic installations. in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Oh dear, I missed the date!!!
Replies
6
Views
593
  • Question
I don't think it will work with only one stake unless some meters have different operating parameters. It doesn't necessarily have to be a stake...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top