Hi all testing of new build house. When carrying out IR testing on circuits unplugged all equipment and took down smoke alarms. As there was a lot of lights connected with lamps and installed in twin and earth. I put live and neutral together and tested to Earth. IR test was starting off low but eventually got above 200mega ohm. So recorded that but got me thinking will the fact that the surge protector was still connected that will make the readings go all over the place. Every circuit got above 200mega ohm which I was happy about but would this surge protector affect readings ? Also find a lot of sparks very rarely carry out IR tests just rely on RCBOs or RCDs ? Hope use can help
 
In the real world, on site, it is often not practical for a L-N test to be carried out as part of the initial verification
Yes, sadly that is the way it is going with most lights being assemblies where you can't remove the electronics from, and where there is not any provision for easily disconnecting it.

I intensely dislike the replace-whole-light-assembly way of the world and would always prefer removable lamps, as it is a waste of resources and adds to testing problems, but for many cases like bathrooms it is hard to get anything IP rated that way.
 
Well I claim to do L-N tests on initial verification each and every time. Not an issue if done at the right time. Seeing Youtubers I get the impression that they wire up/re-wire, fit all accessories the think about testing and that might be becoming more and more the 'norm'. See 641.4 - every installation must be inspected and tested during erection and on completion before being put into service...
 
Well I claim to do L-N tests on initial verification each and every time. Not an issue if done at the right time. Seeing Youtubers I get the impression that they wire up/re-wire, fit all accessories the think about testing and that might be becoming more and more the 'norm'. See 641.4 - every installation must be inspected and tested during erection and on completion before being put into service...
Not doing a L-N test does not mean the installation has not been inspected and tested. There is a compliant LN-E method. How then do you verify you have not caused a low IR L-N after fitting lights/accessories?
The reality is the complication really only applies to lighting circuits, other circuits are simple to test L-N and there is little excuse not to.
 

Reply to IR testing on new build in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top