IR testing through transformer | on ElectriciansForums
Discuss IR testing through transformer in the Talk Electrician area at ElectriciansForums.net
sunderland uk
Hi all need some help, I've got a panel to test 400vac to transformer but after step down 110vac, do i megger it all at 1000v or just ignore transformer and megger at 250vac?
If it is an isolation transformer an IR test on the primary side will have no effect on the secondary. IR tests should be carried out at twice the nominal voltage.
Reply to IR testing through transformer in the Talk Electrician area at ElectriciansForums.net
There is a lock on it, press the test button down and press the lock button, the symbol will appear on the screen in the middle right hand side...
That is very cool. It would be the end user software that would make that the absolute king.
    • Winner
    • Informative