IR testing . . . | Page 2 | on ElectriciansForums

Discuss IR testing . . . in the Australia area at ElectriciansForums.net

D

doodarr

Hi Guy's totally new to website.

Quick question. Doing a new install and the IR for N-E is 87.6 M ohms for first half of the split board. L-E & N-L are both >500 and the complete second half of the board is >500 for all results.
Could it possibly be how close the wires are in the CU giving a lower reading. I'm not worried and know all results pass regs but its just for my own satisfaction. :eek:
Thanks
 
Last edited by a moderator:
BluSparx,

The lights and bolier are not yet connected therefore I could only test the 20A Radials which were fully installed. They will be re-tested again at the weekend along with the rest of the tests for a full re-wire before energised and after lights and boiler have been connected to new CU.
I know how to test IR which is how I got the results . . my question was any idea's why the N-E IR was lower on the 1st bar than the 2nd when tested.
I also said I hadn't retested - as in disconnected everything on bar 1 and earth to check which MCB was dragging the IR down as was suggested on here.
Trying to get the results perfect and improve my knowledge thats all.
This was all explained in the previous posts.

TBF I understand what your asking but as I said unless you test individually you would not be able to complete your test cert correctly. I get sick of seeing made up results on test certs that are so obvious it beggers belief.

If you had tested individually first your circuit dragging the readings down would have given you a clearer indication of where the problem lies, if all the circuits where fine then it could be a problem with a loose connection, the bar screws etc.

Also the questions that are asked on the forum from "sparks" sometimes makes me wonder how people managed to complete there courses and qualifications.

I aint having a pop at you but IR testing and identifying the cause for low readings should be pretty straight forward
 
It is straight forward. One ofthe easiest tests there is. I never make up results which is why I was annoyed that my results weren't >500.
just after some original ideas for any reasons why that could be before I go back. 2 heads is better than one etc.
That's what I thought the forum was for ----ing ideas about. I'm new so sorry if it isnt.
 
Have you split the circuit?

I would test individually to Identify which circuit it is pulling down your value and check terminations. I'v had it before where insulated cables crushed in the backbox have brought down readings.

Rich
 
TBF I understand what your asking but as I said unless you test individually you would not be able to complete your test cert correctly. I get sick of seeing made up results on test certs that are so obvious it beggers belief.

If you had tested individually first your circuit dragging the readings down would have given you a clearer indication of where the problem lies, if all the circuits where fine then it could be a problem with a loose connection, the bar screws etc.

Also the questions that are asked on the forum from "sparks" sometimes makes me wonder how people managed to complete there courses and qualifications.

I aint having a pop at you but IR testing and identifying the cause for low readings should be pretty straight forward

A tad harsh I feel...as far as I can see the OP knows how to carry out IR tests and knows what results to expect...he has not claimed to be an expert and is clearly trying to improve his testing knowledge...nothing wrong with that as far as I can see.
 
agree there , wp, OP is part way through his testing, if i read his posts correctly and has come across a lower than expected reading. this could be ,as previously suggested, a squashed cable , or even a socket face that has been exposed to moisture prior to fitting.
 

Reply to IR testing . . . in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
943

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top