Im completing a EICR for an empty shop which is over 3 floors, TNCS 250Amp TP+N supply which feeds a MCCB board, there is a MCCB per floor plus the lift, the tails into the MCCB board are in galv trunking and the supply up to the floors are wired in SWA.
We wanted to test the insulation resistance at same potential on one of the boards, (Single Phase) with the main switch off, the incomming earth disconnected and a link between the neutral bar and line we tested but this returned a 0.00M Ohm reading.
Thinking the mistake being not opening the neutral link at the MCCB board we went down to the MCCB board, (basement) we isolated the supply and opened the neutral link and had the incomming earth disconnected for Ze, we measured continuity between the neutral bar and the earth bar in the MCCB board and measured 0.18 Ohm, obviously a insulation resistance test would just return a 0.00M Ohm reading so we needed to find out what was causing the continuity, we disconnected the bonding to the water and gas but we're still measuring 0.18 Ohm.
Have I missed something stupidly obvious, there is obviously a connection between neutral and earth somewhere but I havent found it as yet