Hi All- New to this - loving the challenges!

EICR'd my house and found one of my ring finals had an IR problem- just getting to grips with testing and trying to gain experience- college was good, however, felt like it was more of learning to pass exams!

My ring final has an issue- if i test with breaker open-(off) L(load side of breaker) to E (earth bar) = good reading, N(neutral bar) to E= good reading- but L to N a bad reading. so if a possible dead short between L-N why doesn't breaker trip?

However, if i do a IR L and N to E i get a good result!

Sorry for my inexperience but can anyone help me?
 
nope checked that- has spots in bedroom connected somewhere, but left that part of circuit open,
why a good IR reading with the L-N to E:?
thanks for the reply

lol lots of diy bodges (not mine)! even got an off peak socket! spur'ed off eco10 lol
 
definitely sounds like something still plugged in, did you do end to ends on ring final as had similar when i moved in - one side of ring and immersion heater feed transposed so low ir reading ( imm and ring on 32a mcb and 16a mcb nearly got zapped changing imm stat so did pir and found lots of horrors - funny had just been passed by council contractor)
 
Also the reason you'll have a good reading between both live conductors to earth is because there's obviously no fault to earth hence why it seems like an appliance plugged in because otherwise your ring would trip.
 
ty for replys only 2nd post i think!- will investigate further in loft- also for experience going to take all sockets off and connector block them- do a bell test to check continuity then do IR test- end to end- then cutting circuit into 2 and so on.
 
Because if there was a fault to earth you would have a reading between l+E and or N+E but because there isn't a fault present you will get a good reading, because you're getting a reading between N+L this either means there is a fault but more likely you're getting the reading from a load and the connection between L+N is across the load
 
If your getting a good reading when connecting L&N and testing to Earth then i wouldn't be losing any sleep over it, However as mentioned above the readings defiantly insinuate that something is still plugged in to warrant poor readings. If your L&N to earth is over 1.0 meg then as long as your record how its been tested on the test sheet then that's sufficient.
 

Reply to IR Testing??? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
764

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top