When IR testing on lighting circuits i keep coming across dead shorts between L+E and N+E on the same circuit. I then proceed to investigate and the faults clear (maybe a screwed neutral or something ). however im scratching my head as to why im getting dead shorts between L+E when the mcb holds in fine Electrical Trainee syndrome). any advice on this would be fantastic !
 
When you say 'dead shorts' can you give further info? Are you seeing a dead short with the megger at 250/500/1000v or are you seeing a dead short with a normal tester on ohms scale? Once the fault has cleared what reading are you getting on the circuit with the megger and at what test voltage?
 
Last edited:
Yea, dead short.
I always got a slap for saying that.
Had to say zero zero zero, representing 0.00.
Or as the 2391 lecturer used to say, a fault of negligible resistance exists.

Boydy
 
the readings i am getting on my completely disconnected from the board cable is 0.00Mohms (dead short). I am expecting to get >299Mohms when clear at 500v as its a new install. My tester was calibrated 2 weeks ago. any reasons im picking up dead shorts between L+E ? TA
 
Umm, as already mentioned, 0.00 MOhms is not necessarily a dead short, have you tried measuring on the MFT's continuity setting?
 

Reply to IR testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

Similar threads

Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
439
TerryBNZ
T
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top