Hi fellow electricians,


I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?
Also why does the RCD or MCB not trip straight away? What factors affect the circuit to the point that the RCD or MCB decides it's time to trip if there is not a dead short and there is no faulty appliance?


Finally, can someone confirm that the best way to find the furthest point on a ring in which to split the circuit in half is the socket with the highest Zs.


All contributions are appreciated
Many thanks
 
Hi fellow electricians,


I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?
Also why does the RCD or MCB not trip straight away? What factors affect the circuit to the point that the RCD or MCB decides it's time to trip if there is not a dead short and there is no faulty appliance? ohm's law. R=V/I, so R=230/0.03, = 7666.66666667 ohms.
Finally, can someone confirm that the best way to find the furthest point on a ring in which to split the circuit in half is the socket with the highest Zs. not an exact method. better to dead test the resistance on low ohms.


All contributions are appreciated
Many thanks

my comments in red.
 
Thanks Telectrix, took me a while but I finally got it (I think)
So the results need to be as low as 7.6M ohms before the RCD trips. So if I test a circuit and I get 50M ohms why does it trip after a while?

Not sure if Nickblake and Murdoch are taking the mick...

GGF you're only as good as the experience you've had lol I'll keep testing...
 
no 7666 OHMS not MOhms...
intermittent fault, damp ingress into a light fitting, chafed cable etc etc (had a weird one once, only tripped at random times, checked a light fitting which was alright...looked above...with the torch...copper glinting back in the darkness...socket cable had been damaged through chafing, and everytime someone trod on the floor above the cable it was enough to move the cable and cause the rcd to ping out...)
 
See I was always too embarrassed to ask how many digits in 1 meg, I kinda feel stupid now but I better get it straight before I move on, 1st year stuff I know.
1000 ohms is 1 Kohm? 1,000,000 ohms is 1 Mohm?
So when my meter says >999 M it's greater than 999 million ohms?

Thanks overskilled

I have a megger 1730, I done a fault find today and IR said 0.51 on the ring. After an hour and a half of investigation I found a cupboard behind the f/f with a neon switch in the on position. Turned it off and it took my readings up to 160. So I put everything back together everything still unplugged and switched off and results dropped to 50. So this is why I'm asking these questions. I have to go back and rectify the fault but just wanted confirmation the RCD is not going to trip in the middle of the night.
 

Reply to IR Tests & Fault Finding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
769
SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top