Hi fellow electricians,
I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?
Also why does the RCD or MCB not trip straight away? What factors affect the circuit to the point that the RCD or MCB decides it's time to trip if there is not a dead short and there is no faulty appliance?
Finally, can someone confirm that the best way to find the furthest point on a ring in which to split the circuit in half is the socket with the highest Zs.
All contributions are appreciated
Many thanks
I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?