Hi fellow electricians,


I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?
Also why does the RCD or MCB not trip straight away? What factors affect the circuit to the point that the RCD or MCB decides it's time to trip if there is not a dead short and there is no faulty appliance?


Finally, can someone confirm that the best way to find the furthest point on a ring in which to split the circuit in half is the socket with the highest Zs.


All contributions are appreciated
Many thanks
 
I'm intrigued. Your website offers a complete range of services including fault-finding, installations, testing, the whole 9 yards. Is this your company? Daz
 
[ElectriciansForums.net] IR Tests & Fault Finding
 
Hi fellow electricians,


I'll get straight to the point.
How low do the readings for an IR test need to be on 250V or 500V scale before a 30mA RCD or 32A MCB trips when the circuit is live and in operation and where would I find that information? I know it will trip straight away with a dead short but if I get 50M ohms for example on the dead test and then liven the circuit up is it likely to trip after a certain period of time?
Also why does the RCD or MCB not trip straight away? What factors affect the circuit to the point that the RCD or MCB decides it's time to trip if there is not a dead short and there is no faulty appliance?


Finally, can someone confirm that the best way to find the furthest point on a ring in which to split the circuit in half is the socket with the highest Zs.


All contributions are appreciated
Many thanks

????
:smilielol5:
 
0.26 is normally a neon & 0.23 can be electronic piece of equipment still on the circuit, so if you get a low reading around this point always worth having a further look to see if everything is unplugged.
 

Reply to IR Tests & Fault Finding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
770
SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top