IR variable results new install. | on ElectriciansForums

Discuss IR variable results new install. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Feb 28, 2009
Messages
44
Reaction score
5
Any ideas gratefully received.

I'm testing a new ground floor extension. Brand new lighting circuit. Live switches. Only feeding jcc fgled6. Continuity is fine. 0.33 at furthest point. Circuit disconnected from the cu I've had readings from 88MOhms to >299MOhms line/cpc. The others are fine. Being <1Mohm I became paranoid and began testing each leg. Each leg comes back >299MOhms but when I start bunching the cpcs into the terminal or croc clipped IR reading begins to drop off. It's wired in 1mm with 22 downlights the load being 1.8amps if they're all on. Ceiling void is insulated celotex and cable clipped direct or capped and in plaster. Multiple two way and intermediate switches.
It's not too hot today 23 degrees ambient but reasonably humid as tiling has been laying the large floor space.

Any ideas as I want to go home now!
 
The lights aren't connected at the moment hence why I'm still here. Today's job was to get them all connected and the builders beginning to roll his eyes!
 
They've been plastered but they're dry enough to have a mist coat put on in the majority of the room with no obvious damp plaster patches visible elsewhere.
 
If that is the case with the low uncertifiable readings do I just grit my teeth and put down the highest I've had????
its not the best situation I've found myself in.
 
Honestly I know it's pretty hot at the moment but plaster still takes a bit of time to cure and go off, and what you wrote would indicate to me that your getting these spurious reading via damp plaster.

Now you never heard this from me but if you have RCD protection on the circuit, bypass it and fire them up for a while. I'll be betting your results improve within a few hours
 
Didn't hear a thing!! ;-)
It crossed my mind but they drill dead test dead test dead test.
Hmm I'll start fitting the lights then. Could be worse they're push fit!
 
If it is all brand new wiring then are you sure you want to accept 88Mohms? For an old installation ok, but brand new?

This is where an analogue IR tester is really useful, you can tell by the needle movement whether it's just damp or actually something untoward.

How long did you test the circuit for? was it a quick test and go or did you test it for 1 minute or at least wait until it had fully stabilized?
 
Are the low IR readings on just one circuit or did you test with other circuits? What was R1+R2 as I make 0.33ohms for R2 in 1mm less than 20m which seems odd for circuit with multiple intermediate and 2way switches? Did you IR test when operating switches to see if that narrowed it down? Sounds like you've had a long day, under pressure and I would imagine if you returned tomorrow you'll 'kick yourself'! Good luck!:smiley2:

Edit, were cpc's connected at board as it seems to say 'circuit disconnected at CU' or was this after low readings
 
Last edited by a moderator:
If it is all brand new wiring then are you sure you want to accept 88Mohms? For an old installation ok, but brand new?

This is where an analogue IR tester is really useful, you can tell by the needle movement whether it's just damp or actually something untoward.

How long did you test the circuit for? was it a quick test and go or did you test it for 1 minute or at least wait until it had fully stabilized?


Totally lay agree with you re results

ive got a digital analogue display it flits about all over the place or creeps up slowly all the way to >299MOhms
 

Reply to IR variable results new install. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
346
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
885
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top