Is 0.75mm Flex in conduit behind tiles and tile backer sufficient for led lights (6w) or Fan (4w)? | Page 2 | on ElectriciansForums

Discuss Is 0.75mm Flex in conduit behind tiles and tile backer sufficient for led lights (6w) or Fan (4w)? in the UK Electrical Forum area at ElectriciansForums.net

benhurr

DIY
Joined
Sep 16, 2022
Messages
69
Reaction score
10
Location
harrow
Hello to all.
I know now that 1mm T&E would be better for lights, but legally is 0.75mm Flex in conduit behind tiles and tile backer sufficient for led lights (6w) or Extractor Fan (4w)?
1 out of 3 quoting electricians said that those need to be replaced. Is it really that bad? Looking at the specs it is more than sufficient (0.75mm handles 6amp 1380 Watt) and not being exposed to movement and covered by conduit etc.
 
Fused connection unit.

What is a maintenance switch?
Fused spur switch ?

I think here is the answer suggestion that 0.75 on lighting is acceptable .75mm flex used from junction box to downlights - https://www.electriciansforums.net/threads/75mm-flex-used-from-junction-box-to-downlights.171264/
or maybe they are referring to an older regulations.
I can see now the reg It is clearly saying 1mm for lighting circuits 220v :( regardless of flexing.
But how about this way:
We remove the led driver from light fitting and place it in a box outside the room, this way it is going to be low voltage going via 0.75mm with is within current regulations.
The wire is less than a meter long.

To be honest it doesn't make much sense if this flex 0.75mm allowed on flexible applications like hanging lights but not good inside the wall in conduit behind tiles and backing board (even if it will be very short part of it)
 
Last edited:
If it's in conduit the electrician can just use the bit of flex to pull through whatever cable they feel is required.

We can all give you our own opinions on what is/is not acceptable but ultimately it is down to the electrician who does the work and signs it off to make the decision and put their name to it.

A lot of electricians are likely to refuse to connect or sign off a cable which the customer has installed themselves regardless of what size or type it is.
 
But how about this way:
We remove the led driver from light fitting and place it in a box outside the room, this way it is going to be low voltage going via 0.75mm with is within current regulations.
If it's in conduit the electrician can just use the bit of flex to pull through whatever cable they feel is required.

We can all give you our own opinions on what is/is not acceptable but ultimately it is down to the electrician who does the work and signs it off to make the decision and put their name to it.

A lot of electricians are likely to refuse to connect or sign off a cable which the customer has installed themselves regardless of what size or type it is.
 
Interesting. The way I read table 52.3, from left to right, 0.75mm2 flex is permitted.

Do you mean the bottom section for single appliances and other applications?

It is my understanding that this really relates to the final aspects, such as pendant drops etc rather than fixed wiring
 
Do you mean the bottom section for single appliances and other applications?

It is my understanding that this really relates to the final aspects, such as pendant drops etc rather than fixed wiring
I do indeed mean the bottom section, but I have selected 'flex' from column 1 first, then 'any other application' from col 2 (I assume this means 'any application other than those others listed for flex'), which gives me 0.75mm2 from col 3.

It seems logical to me to work from the table in this order, rather than working from the middle outward (though the table really could be clearer on this).

I had also assumed that the minimum 1mm2 was for non-flexible cables due to smaller conductors being prone to damage, either during installation or in use, whereas this wouldn't be a problem for flexible cables.
 

Reply to Is 0.75mm Flex in conduit behind tiles and tile backer sufficient for led lights (6w) or Fan (4w)? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top