Most people have mobile phones with torches ..................
tried that. the phone kept falling off my head.
 
I know of a fire in a new build a few years ago, where the fire was deemed to have been caused by stuck fan blades and the lack of a 3A fuse in the fan supply. Locked rotor current insufficient to trip the 6A MCB supplying the circuit.
 
I know of a fire in a new build a few years ago, where the fire was deemed to have been caused by stuck fan blades and the lack of a 3A fuse in the fan supply. Locked rotor current insufficient to trip the 6A MCB supplying the circuit.
it would probably not have blown a 3A fuse either.
 
they specify a 3A fuse because they don't have a clue about OCPD discrimination. a 1A fuse would be more appropriate.

i'll give you a personal example. i had a vivarium with a 250wall heat/light reflector lamp. plug fuse was 5A. when the lamp blew, it took out the 16A MCB in the CU, leaving the 5A fuse in the plug intact.
 
Presumably the collapsing filament produced a near short circuit, otherwise nothing would have blown/tripped. Under those circumstances a type B MCB probably would trip faster than a plug fuse would rupture. The stuck fan motor would pass a sustained current of a few amps which is a completely different scenario.
On a related subject, there have been many threads on here concerning MCBs in series, and their lack of discrimination. While this may be true when short circuits are considered, a lower rated second MCB in the chain will discriminate against overload.
 
I know of a fire in a new build a few years ago, where the fire was deemed to have been caused by stuck fan blades and the lack of a 3A fuse in the fan supply. Locked rotor current insufficient to trip the 6A MCB supplying the circuit.

Then the manufacturer should have fitted appropriate protection within the fan, the ocpds we install are not there to protect appliances, they are there to protect the cables which feed the appliances.
 
Not sure I'd like to argue that in front of a Coroner's court.
Fortunately, in the case I referred to, no Coroners were involved, although the property in question received serious damage to its roof, and presumably, water damage throughout the rest of the house.
I normally only fit triple pole fan isolators alongside in line fans in lofts, and supply the whole lighting circuit to the bathroom through a switched FCU, fitted with a 3A fuse as per most manufacturers instructions.
Wall mounted fans, which I try to avoid because of their comparatively poor extraction rate and noise, just get the switched FCU.
 

Reply to Is a Fan isolator required in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

D
Hi all, I'm looking for recommendations for a kitchen extractor fan with a rate of 60l/s. We're nearly done with our renovation, but we've just...
Replies
0
Views
171
dimmi1975
D
Thanks very much, also a good tip :)
    • Like
Replies
4
Views
351

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top