C
cripster
Oh and thanks... Thats all what I basically wanted to know. Thanks High Tower!
No i mean the main cover that covers all of the guts, this burning almost certainly started at one of the terminals.
so why are you arguing with me then?
i'm not, you're just wrong.
see you later.
conversation i had with a builder today went something like this...............
you can't put that shower in the bathroom.
why not?
because it's 10.8kw and your cable's only 6 mill' squared.
so what?
so you need a bigger cable or a smaller shower.
why?
because the shower you've got has a FLC of over 45A, and your cable is only rated at 38A.
it'll be alright.
no it won't.
'course it will.
well, why did you ask me then?
because i wanted your advice.
so why are you arguing with me then?
i'm not, you're just wrong. everyone knows a shower's wired in 6mm cable.
see you later.
Crisper out of interest what was the rating on the existing shower, in KW?
P.S. I'm just doing the 'donkey work' a sparky mate will connect and test and certify the dangerous stuff.
Naughty, naughty, not reading the whole thread :90:
He told us what the rating was at the start... 10.4kw
:artist: