I may get my head bitten off for this, but please be nice. I want to get the supply to my cooker replaced from 6mm to 10mm, but the existing route is almost impossible, but there is an easier route following the vent/stench pipe (that is boxed in ) through the bathroom and into the loft, then across to the front of the house and back down to the consumer unit. One company said they cant do it, as it passes through the bathroom, another has said it's ok because the cable is not part of the bathroom, and the boxed corner is completely built into the wall, I want to run the cable myself and get the electrician to do the final burying of the cable in the kitchen wall for the last 1.5 metres, and the final installation at the consumer unit with a new breaker, neither have an issue with that, its just the cable running down the boxed in pipework- Can anyone tell me if there are any regulations that it breaches? Thanks
 
OK, to throw more lights on the subject, we are looking at replacing our existing standard cooker with a range type cooker, as our family is 2 adults and 4 teenagers, something like a BELLING Classic 100 Electric Range Cooker , and was informed by a friend (not an electrician) who done the same to check the supply, as he had trouble with his until they upgraded the cable. I know a little bit about electrics, as have done a C&G mechanical to electrical engineer multi-skill course, enough to know I am not qualified to mess about in the consumer unit, or make decisions about cable routes, but am more than capable or routing the cable through my house. As for finding an electrician I can trust, this is the first time I have needed to use one, and when 2 give opposite answers, I like to give my work to the one that is right, and hopefully then I can trust them, and I thought it was a bit strange about the cable not being allowed to run through the bathroom ( being as the ceiling lights for the kitchen underneath must be in a similar environment?). At the moment it's connected to 6mm cable with a 32 amp breaker, and was told it should be OK, but may have issues if everything is running??
 
Just checked that cooker and max it will draw is 5kw. That's 20A at 230v and 25A at 254v.

6mm cable is fine mate!
your friend prob had 2.5mm cable in which is not suitable. Most older houses had the cooker connected to a socket ring.

yours is fine mate.

just make sure you have RCD protection and earth bonding!
 
My question same as last 2, why are you changing to 10mm unless your cooker is over 8.5kW?
i have never had a cooker require a 10mm cable (except a commercial/industrial cooker!)

Neither had I until a few weeks ago when I fitted a gas pipe and radial at my mate's house for the gas hob and electric oven he was getting, then this bloody big all electric range cooker thing arrived - rated at 11kW ............ :32:
 
Applying diversity to the 13.5kW max load we're talking either 22A or 27A if the cooker switch has a socket on it. Funnily enough I personally wired in a Belling 100 for a mate a few weeks ago on his existing 6mm and 32A breaker. He's had no problems at all.

Whoever wants to run 10mm is tring to pull a fast one! Either that or they are just another incompetent Electrical Trainee with no idea whatsoever about even the simplest aspects of circuit design.
 
as i've already said. 6.0mm on a 32A MCB will handle any domestic cooker. anybody heard of diversity?

Interesting, I've done two domestic kitchens with wolf ranges rated at 50A before any diversity is applied. Wired in 10mm on a 45A breaker the first time and low and behold it took it out when it was running on full chat!
It did indeed run draw the full 50A when it's self cleaning cycle started up.

I can only imagine how happy the client would be if I'd followed a blanket 'domestic cooker is always 6mm' rule!
 

Reply to Is it ok to run cable within a boxed vent pipe? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
832
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
682

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top