I am planning a new layout for our utility room and would appreciate some advice. We have three appliances (washer, dryer and freezer) that will sit under a worktop directly below the window. My intention is to feed this equipment via a row of three 13A fused spur switchplates located inside a tall larder unit to the right of the appliances.

Would there be any problem in terminating each of these switched fused spurs with an unswitched 13A socket instead of cutting off the moulded plugs currently fitted to the appliance power cords and hard wiring each cable to a flex outlet box?

Another issue is the risk of trapping the mains cord when one of these big and heavy machines is pulled out from under the worktop for servicing and then pushed back. There will only be a 23mm gap between each machine, so it will be impossible to see what is happening behind the appliances. The only solution I can think of is to pull the loose mains cord up and across the top of the machine before it is pushed back under the worktop. The loose cable would then be pushed back out of sight once the machine is in place.

Are there any better ways to minimise the risk of trapping the cable?
 
This would be my preferred option too; a new 32A radial circuit (A2 if I'm not mistaken) to supply the appliances alone; I'd also prefer to see one fuse only for each appliance so either 20A DO switches for isolation & unswitched 13A sockets for connection or Switched FCUs and flex outlets.
 
... I would say that ventilation for the freezer is your biggest concern and you may need to put a vent in the worktop above it.

The manufacturer of my new washing machine and dryer has told me that it is fine to enclose each of these machines in what is essentially a box with an open front (all my appliances will have a decor panel on each side and a worktop running over the top). However, I have not yet checked the ventilation requirements for my old freezer.

This would be my preferred option too; a new 32A radial circuit (A2 if I'm not mistaken) to supply the appliances alone; I'd also prefer to see one fuse only for each appliance so either 20A DO switches for isolation & unswitched 13A sockets for connection or Switched FCUs and flex outlets.

I will be using dedicated 20A FCUs connected to flex outlets for each of the three appliances. At present, they are temporarily connected into existing 13A ring main sockets in our utility room. This ring is also used for our CH boiler, but not much else of any significance. No fuses have tripped so far...

It's a long time since I read the IEE Regulations. Is your advice to use a dedicated 32A radial circuit for laundry appliances generally considered to be the correct method?
 
The ring main in our utility room also serves two small spare bedrooms and the attic, where it feeds a TV aerial amp and a pair of 99W extractor fans for bathrooms. The loading is so low that you could argue that connecting the washer, dryer and freezer to this ring would be better than a dedicated radial circuit, as the current would flow through two wires instead of one.
 
This would be my preferred option too; a new 32A radial circuit (A2 if I'm not mistaken) to supply the appliances alone ...

I've now calculated the max current loading generated by the washer, dryer, freezer, CH boiler, and two Xpelair fans connected to my utility room ring main as being under 18A. A dedicated radial circuit seems unnecessary.

... I would say that ventilation for the freezer is your biggest concern and you may need to put a vent in the worktop above it.

I've also just found my Zanussi freezer manual, which tells me that a solid worktop above the freezer is only acceptable if the gap below the worktop is 50mm and there is a 25mm gap on each side (alternatively, you need a top gap of at least 100mm if there are no side gaps).

I can't meet those conditions, so I will need to put a vent in the worktop. Many thanks for alerting me to that issue.
 
Do the English Building Regs not require above counter top isolation like the Scottish Building Standards?

As far as I'm aware, there's nothing in the England & Wales Building Regs (Wales uses 2010 version) requiring above counter top isolation. BS7671 553.1.7 ...all equipment can be supplied from an adjacent accessible socket outlet...... The socket outlet should be accessible before removing a built in appliance (not sure of the reg on that one). I even seen some suggest, that an mcb is a form of isolation, if its nearby, not that I'm convinced of that one.
 
Do the English Building Regs not require above counter top isolation like the Scottish Building Standards?

In one word - NO.

That said including a definition of accessible in BS 7671 woudn't be difficult AND a socket behind the appliance is not accessible IMHO.

I think the OP needs to discuss this with the kitchen fitter AND a spark .... internet based advice can't see whats actually happening.
 
As previously stated, I no longer intend to have sockets behind the appliances. The current plan is to have flex outlets fed from three FCUs. Those FCUs cannot be located directly above the worktop as that space is fully occupied by a window, so I want them to be put inside a tall larder unit to the right of the row of machines, where they would be placed at a slightly higher level than the worktop.

Gaining access to the FCUs would thus just be a simple matter of opening the larder door.
 
What exactly do you mean by 'above counter top isolation'?
Exactly what it says. It’s also a mandatory Reg in SBS. But tbh our Building Regs are easier laid out and easier to follow than England/Wales. Part P and all that nonsense. As you don’t appear constrained by that rule you have free reign.

BTW, the IEE Regs don’t refer to it as a ring main. It’s a ring final circuit you are describing
 
I'm well aware that the IEE Regs use the term ring final circuit, but ring main has been common terminology since Adam was a boy - and it has the advantage of being shorter and easier to say. Old habits die hard! :)

Very few phrases in the English language are totally unambiguous and 'above counter top isolation' certainly fails that test. Taken literally, it means directly above, rather than simply at a higher level, but words are not always meant to be interpreted in such a literal manner. Just out of interest, does the layout I described in my previous post meet the Scottish regs?
 
Would worry about it passing Scottish regs; their stuff is different, something to do with the weather and those large midges.:)

I hail from north of the border and have plenty of experience of Highland midges, but large they are not. The pesky blighters are tiny creatures. The irritation they cause is out of all proportion to their size.
 

Reply to Is it OK to terminate switched fused spur with 13A socket? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
647
It depends on where that SFU 'sits' in the circuit. If it's there as a courtesy isolator for the fridge socket then potentially yes as it could...
Replies
2
Views
794
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
1K
  • Question
I’ll agree with Tel…. Change it to a more useful single socket. Did I just say that I agree with Tel???? 😆
Replies
5
Views
2K
  • Question
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
    • Like
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks