I am planning a new layout for our utility room and would appreciate some advice. We have three appliances (washer, dryer and freezer) that will sit under a worktop directly below the window. My intention is to feed this equipment via a row of three 13A fused spur switchplates located inside a tall larder unit to the right of the appliances.

Would there be any problem in terminating each of these switched fused spurs with an unswitched 13A socket instead of cutting off the moulded plugs currently fitted to the appliance power cords and hard wiring each cable to a flex outlet box?

Another issue is the risk of trapping the mains cord when one of these big and heavy machines is pulled out from under the worktop for servicing and then pushed back. There will only be a 23mm gap between each machine, so it will be impossible to see what is happening behind the appliances. The only solution I can think of is to pull the loose mains cord up and across the top of the machine before it is pushed back under the worktop. The loose cable would then be pushed back out of sight once the machine is in place.

Are there any better ways to minimise the risk of trapping the cable?
 
I've just checked the specs for my dryer and washing machine.

The 'total rated load' of the dryer is 1.1kW, while the washing machine is 2.1-2.4kW. That suggests the latter might generate more heat.

However, the dryer's energy consumption for the 'Cottons Normal dry standard programme' with a full load is given as 1.39kWh, while the washing machine's energy consumption for the 'Cottons 60° standard programme' with a full load is 1.0kWh.
 
Power in does not necessarily equal heat out. The dryer blows most of the heat out of the front vent (remember to clean out the fluff every time you use it), while the freezer needs airflow over the heat exchanger at the back or it will not work. The washing machine will not get very hot at all - even a hot wash is only 60 degrees and most are set at 40 or less.

Insulation on appliances is much better these days too - my old dishwasher would melt butter left on the worktop above it, while the newer one does not even feel warm to the touch.

I would say that ventilation for the freezer is your biggest concern and you may need to put a vent in the worktop above it.
 
I may well be wrong on this, but I would imadgine that the freezer will also have to work harder if the environment surrounding it is warmer, as some of that heat will make it through the insulation to the inside and the heat pump will become less efficient in warmer ambient air. Im not sure how much of an impact this will have in the real world, however.
 
The Freezer is trying to remove any residual heat from the produce in the freezer compartment, and dissipate this heat via the evaporator plate at the back of the appliance. Should this evaporator become dirty, blocked then the appliance will be less efficient, so it is imperative to ensure the evaporator is kept free from dirt, dust etc basic physics in essence.
 
This would be my preferred option too; a new 32A radial circuit (A2 if I'm not mistaken) to supply the appliances alone; I'd also prefer to see one fuse only for each appliance so either 20A DO switches for isolation & unswitched 13A sockets for connection or Switched FCUs and flex outlets.
 
... I would say that ventilation for the freezer is your biggest concern and you may need to put a vent in the worktop above it.

The manufacturer of my new washing machine and dryer has told me that it is fine to enclose each of these machines in what is essentially a box with an open front (all my appliances will have a decor panel on each side and a worktop running over the top). However, I have not yet checked the ventilation requirements for my old freezer.

This would be my preferred option too; a new 32A radial circuit (A2 if I'm not mistaken) to supply the appliances alone; I'd also prefer to see one fuse only for each appliance so either 20A DO switches for isolation & unswitched 13A sockets for connection or Switched FCUs and flex outlets.

I will be using dedicated 20A FCUs connected to flex outlets for each of the three appliances. At present, they are temporarily connected into existing 13A ring main sockets in our utility room. This ring is also used for our CH boiler, but not much else of any significance. No fuses have tripped so far...

It's a long time since I read the IEE Regulations. Is your advice to use a dedicated 32A radial circuit for laundry appliances generally considered to be the correct method?
 
The ring main in our utility room also serves two small spare bedrooms and the attic, where it feeds a TV aerial amp and a pair of 99W extractor fans for bathrooms. The loading is so low that you could argue that connecting the washer, dryer and freezer to this ring would be better than a dedicated radial circuit, as the current would flow through two wires instead of one.
 
This would be my preferred option too; a new 32A radial circuit (A2 if I'm not mistaken) to supply the appliances alone ...

I've now calculated the max current loading generated by the washer, dryer, freezer, CH boiler, and two Xpelair fans connected to my utility room ring main as being under 18A. A dedicated radial circuit seems unnecessary.

... I would say that ventilation for the freezer is your biggest concern and you may need to put a vent in the worktop above it.

I've also just found my Zanussi freezer manual, which tells me that a solid worktop above the freezer is only acceptable if the gap below the worktop is 50mm and there is a 25mm gap on each side (alternatively, you need a top gap of at least 100mm if there are no side gaps).

I can't meet those conditions, so I will need to put a vent in the worktop. Many thanks for alerting me to that issue.
 
Do the English Building Regs not require above counter top isolation like the Scottish Building Standards?

As far as I'm aware, there's nothing in the England & Wales Building Regs (Wales uses 2010 version) requiring above counter top isolation. BS7671 553.1.7 ...all equipment can be supplied from an adjacent accessible socket outlet...... The socket outlet should be accessible before removing a built in appliance (not sure of the reg on that one). I even seen some suggest, that an mcb is a form of isolation, if its nearby, not that I'm convinced of that one.
 
Do the English Building Regs not require above counter top isolation like the Scottish Building Standards?

In one word - NO.

That said including a definition of accessible in BS 7671 woudn't be difficult AND a socket behind the appliance is not accessible IMHO.

I think the OP needs to discuss this with the kitchen fitter AND a spark .... internet based advice can't see whats actually happening.
 
As previously stated, I no longer intend to have sockets behind the appliances. The current plan is to have flex outlets fed from three FCUs. Those FCUs cannot be located directly above the worktop as that space is fully occupied by a window, so I want them to be put inside a tall larder unit to the right of the row of machines, where they would be placed at a slightly higher level than the worktop.

Gaining access to the FCUs would thus just be a simple matter of opening the larder door.
 
What exactly do you mean by 'above counter top isolation'?
Exactly what it says. It’s also a mandatory Reg in SBS. But tbh our Building Regs are easier laid out and easier to follow than England/Wales. Part P and all that nonsense. As you don’t appear constrained by that rule you have free reign.

BTW, the IEE Regs don’t refer to it as a ring main. It’s a ring final circuit you are describing
 

Reply to Is it OK to terminate switched fused spur with 13A socket? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
928
It depends on where that SFU 'sits' in the circuit. If it's there as a courtesy isolator for the fridge socket then potentially yes as it could...
Replies
2
Views
995

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top