Is it possible to put a 16mm swa on a 40a mcb protected by an rcd | on ElectriciansForums

Discuss Is it possible to put a 16mm swa on a 40a mcb protected by an rcd in the UK Electrical Forum area at ElectriciansForums.net

Is it possible to put a 16mm swa on a 40a mcb protected by an rcd
If you look at the technical information from the MCB manufacturers website you should be able to obtain the maximum cable size that the device can accommodate, I think a typical 40A mcb will accept a 25mm cable but you need to check this. You will also need to check that the neutral and earth conductors can also safely be accommodated n their respective terminals. The issue normally with larger SWA cables is having sufficient space in the enclosure to gland and terminate the cable.
 
It will just be rcd protected at the incoming point and then mcbs at the other end
Poor design. SWA doesn't need protection by a RCD, since there's very little likelihood of making contact with the live conductor, without shorting it to earth, in which case the OCD will take care of things.
Ideally this should be a fuse rather than a MCB, to provide discrimination between it and the MCBs or RCBOs at the load end.
 

Reply to Is it possible to put a 16mm swa on a 40a mcb protected by an rcd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
515
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top