While opinions and advice differ and there is a degree of judgment in all cases, the best and most accessible guide to EICR coding is probably the Best Practice Guide #4:
https://www.----------------------------/media/2149/bpg4-1.pdf
 
While opinions and advice differ and there is a degree of judgment in all cases, the best and most accessible guide to EICR coding is probably the Best Practice Guide #4:
https://www.----------------------------/media/2149/bpg4-1.pdf
Thank you for this
 
I rent a house out and take good care of it. Not all landlords are bad.
Completely understand that mate, I’ve rented in the past just curious as to why so concerned....I’m with you for a decent landlord idve just stuck down and if I liked the client idve made good of whilst doing the EICR so it was never an issue ?
 
The BPG#4 has this under C3:

  • Wiring systems not adequately supported to prevent premature collapse in the event of a fire. Note: In locations other than in individual dwellings, such as communal areas forming part of an escape route, this would warrant a code C2 classification to be recorded)
The clarification is a bit convoluted to me, as it sounds like C2 only non-domestic but I think they mean (or maybe they should mean) C2 for any escape route or likely fireman access route.
 
The BPG#4 has this under C3:

  • Wiring systems not adequately supported to prevent premature collapse in the event of a fire. Note: In locations other than in individual dwellings, such as communal areas forming part of an escape route, this would warrant a code C2 classification to be recorded)
The clarification is a bit convoluted to me, as it sounds like C2 only non-domestic but I think they mean (or maybe they should mean) C2 for any escape route or likely fireman access route.

Seems sensible. A code of C2 force cable in the corner of the bathroom seems harsh.

Mind you, we haven't seen a photo yet have we?
 
Bit of engineering judgement here surely...it’s been there years and isn’t in an escape route of any kind...c3 at worst surely? And it complies at the time of installation...
 
Completely understand that mate, I’ve rented in the past just curious as to why so concerned....I’m with you for a decent landlord idve just stuck down and if I liked the client idve made good of whilst doing the EICR so it was never an issue ?
Now that these EICRs have become mandatory none of the people doing them are doing any work at the time. Well not where my house is. So it seems to me a great money spinner. If it was done at the time it would be simplet
 
Seems sensible. A code of C2 force cable in the corner of the bathroom seems harsh.

Mind you, we haven't seen a photo yet have we?
I am not there as I live elsewhere. 350 miles away. The cable is in the kitchen on adjoining wall. Fridge freezer is about a food away
 
Lot of landlords are getting caught out with sparks treating eicrs as loss leaders.....£90 for a 3 bed house!....lovely till the report comes back ?
 
Now that these EICRs have become mandatory none of the people doing them are doing any work at the time. Well not where my house is. So it seems to me a great money spinner. If it was done at the time it would be simplet
Some of us are doing minor remedial works at the time, by prior agreement, as it saves the landlord time & money. Likely fixing a piece of trunking would fall into that category. However, there are some landlords who want a quote beforehand for everything however minor - those I am not fixing at the time, and it will eventually cost them more.
 
Bit of engineering judgement here surely...it’s been there years and isn’t in an escape route of any kind...c3 at worst surely? And it complies at the time of installation...
Well common sense tells me that. Believe me I have done everything to make the place safe including work that is not mandatory. For example a wired fire alarm system. It's not a house of multiple occupation. I have put in new lights, lots of points etc
Some of us are doing minor remedial works at the time, by prior agreement, as it saves the landlord time & money. Likely fixing a piece of trunking would fall into that category. However, there are some landlords who want a quote beforehand for everything however minor - those I am not fixing at the time, and it will eventually cost them more.
I would most certainly have been happy for the work at the time. I feel that I am being ripped off to be far. And I have used them before to do lots of things
 
Bit of engineering judgement here surely...it’s been there years and isn’t in an escape route of any kind...c3 at worst surely? And it complies at the time of installation...

The 'escape route' part has been changed. It now applies to all wiring.
 
Yep...I was getting at the fact it didn’t when installed mate, don’t get wrong if that was in an escape route I’d c2 it but it’s a bit harsh considering it’s location

As @DPG commented in post #20, I haven't seen any pics of the trunking so it's hard to say mate.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cornwall
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Is loose trunking C2 or C3
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
68

Thread Tags

Advert

Thread statistics

Created
Car123,
Last reply from
Spoon,
Replies
68
Views
6,267

Advert

TrueNAS JBOD Storage Server

Back
Top