Was testing earlier and my measured R1+R2 values decreasing the further I was from the DB...
Turns out I'd nulled with my 30m wander lead earlier, but even though the machine had been switched off it hadn't reset. It was taking every reading and subtracting the 0.50 ohms measured on the long lead. No errors thrown up by the machine, so it was displaying a 0.15 ohm continuity as 0.35 (in reality it must have read -0.35 but my MFT doesn't display a negative symbol...
Is this normal?!
It's a Metrel MI3000...
Turns out I'd nulled with my 30m wander lead earlier, but even though the machine had been switched off it hadn't reset. It was taking every reading and subtracting the 0.50 ohms measured on the long lead. No errors thrown up by the machine, so it was displaying a 0.15 ohm continuity as 0.35 (in reality it must have read -0.35 but my MFT doesn't display a negative symbol...