Hi There,
I have installed a 16A radial circuit into mycustomers loft via a new DB. The current system is a TT system with the Main Bonding Conductor being a 6.0mm. We have noted this to be an issue. However, on testing, the electrode resistance came out as 9.96ohms, and then a Zs on our circuit, being only a couple of meters away, at 9.97ohms.
This is all fed from a new 2 way DB, with a 61008 RCD main switch rated at 63A 30mA trip. The protective device for the circuit is a 60898 Type B 16A. Therefore, with the Zs being at 9.97ohms, does the presence of the RCD main switch rectify this?
Any help would be much appreciated.
I have installed a 16A radial circuit into mycustomers loft via a new DB. The current system is a TT system with the Main Bonding Conductor being a 6.0mm. We have noted this to be an issue. However, on testing, the electrode resistance came out as 9.96ohms, and then a Zs on our circuit, being only a couple of meters away, at 9.97ohms.