Is RCD needed at both ends of armour feed to outbuilding | Page 2 | on ElectriciansForums

Discuss Is RCD needed at both ends of armour feed to outbuilding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

If tncs or tns I would take swa (which is mechcanically protected ) via a main switch 1 way unit to new board in garage with a earth rod and a rcd fitted, or you could use rcd at mains and no rcd at board. I had this conversation with napit who explained it to me, parallel path or something of that nature. Pretty basic stuff
 
Why TT it though ?

With TNC-S/PME this may make financial sense in some circumstances, but with TN-S you could just use 3-core Armoured, use the armour as the CPC the core as the bond (or Vice versa), and keep the RCD local to the outbuilding which is more convenient.

The armoured cable will not need RCD protection, this is what I asked further back " why an RCBO ?"

Edit: the OP is already planning on using 10mm Armoured cable.
 
Last edited:
Hi - first post.

I am going to carry out a sub main installation from a main CU in the house, to a garage, (15m from main CU to garage sub board).

The CU in the house has no RCD protection.
The garage will have a local TT, and the sub board will have 30mA RCD as main switch.
The SWA cable 10mm2 will come off a 45A type B breaker. The steel wire sheath will be earthed via gland/banjo at main CU earth.

My question is: given that all sockets/light ccts in the garage will have local RCD protection - do I need to upgrade the main CU to include RCD or RCBO on the SWA feed to the garage? My thinking is that if someone stabs through the armour there is no RCD protection for the inner conductors.....

No doubt this question has been asked before and apologies if this is old, old ground but is the first time I have installed this arrangement on an old board with no existing RCD.

I am domestic installer 2 years in.

main supply earth is TNS

The garage will have a local TT

they have cold water supply in garage then TT is a must

These are questions I'd expect my first year apprentice to know the answer to!

Some unsuspecting person (I'm assuming you are being paid for this work) has selected you to carry out this work for them, work that could have gone to a fully qualified spark who knows what he is doing! I'm guessing the customer has been mislead to believe that you are qualified. This makes me angry.

Back to the drawing board for you kiddo! I suggest college, 3 years minimum if you want to continue playing around with things that you currently have no knowledge of.
 
Last edited:
I think u are not allowed to take a earth outside of the installation were extraneous conductive parts are bounded creating a parallel path, I am unsure on the specific but I can find this out on Monday give my guy at napit a call. I am pretty much into the solar so I have had to do domestic installation design for a while, I will post my findings on Monday or I am sure one the lads on here may clear it up. I know what you are saying as I would of done that before the napit guy specified a tt
 
I think u are not allowed to take a earth outside of the installation were extraneous conductive parts are bounded creating a parallel path, I am unsure on the specific but I can find this out on Monday give my guy at napit a call. I am pretty much into the solar so I have had to do domestic installation design for a while, I will post my findings on Monday or I am sure one the lads on here may clear it up. I know what you are saying as I would of done that before the napit guy specified a tt

Ballocks, show me a reg that says this,
there is a bit of confusion surrounding TNC-S/PME, some say it is a DNO rule, but it is permissible by BS7671.
 
Ok I will do as it states in my post I will clarify this on Monday I maybe wrong but if my governing body implies this I should at least listen, as I am not apart of the ' I know best ' department as some people will always argue the ----
 
I think u are not allowed to take a earth outside of the installation were extraneous conductive parts are bounded creating a parallel path, I am unsure on the specific but I can find this out on Monday give my guy at napit a call. I am pretty much into the solar so I have had to do domestic installation design for a while, I will post my findings on Monday or I am sure one the lads on here may clear it up. I know what you are saying as I would of done that before the napit guy specified a tt

Extend the equipotential zone then?! Just goes to show how useless these scam assessors are! Mind, aren't Napit assessors the ones that insist on flying earth leads in sockets? What a bunch of morons!

They are not applying BS7671 to their assessments, they are applying 'club rules'. Your responsibility is to ensure that the installation complies with the former set of rules, that is all! If it complies with the former but doesn't comply with the latter then that is an issue between you and them only, your installation still complies with the regs.
 
They are not your "governing body" for a start, and they don't write the regs, you pay them a large amount of money so you can self certify, that is all.
 

Reply to Is RCD needed at both ends of armour feed to outbuilding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
790
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top