Hi can anyone give me any infomation pointers in regards to inspecting and testing a school.
 
Re: Is there any difference in inspecting and testing a school, to a domestic install

Non different! Inspection& Testing is just that no variations!
 
Re: Is there any difference in inspecting and testing a school, to a domestic install

Hi can anyone give me any infomation pointers in regards to inspecting and testing a school.

If you've only got domestic installation experience then I might question your competence for this work, you should be familiar with the type of installation to be inspected.

Are you familiar with 3-phase systems-you will find most schools are 3-phase for kitchen, woodwork, metalwork supplies etc. as well as the general distribution system.

Nightshift/out of hours is a must for obvious safety reasons and you may need access equipment for main hall/gymnasium lighting.

The caretakers can be a great help for locating difficult to find circuits etc. always get a mobile number!

In classrooms, always check behind posters and pictures for switches/sockets, they always get covered up!

Anything else specific, just ask, we do about 40 schools a year!
 
Re: Is there any difference in inspecting and testing a school, to a domestic install

3 phase all ok.
If you've only got domestic installation experience then I might question your competence for this work, you should be familiar with the type of installation to be inspected.

Are you familiar with 3-phase systems-you will find most schools are 3-phase for kitchen, woodwork, metalwork supplies etc. as well as the general distribution system.

Nightshift/out of hours is a must for obvious safety reasons and you may need access equipment for main hall/gymnasium lighting.

The caretakers can be a great help for locating difficult to find circuits etc. always get a mobile number!

In classrooms, always check behind posters and pictures for switches/sockets, they always get covered up!

Anything else specific, just ask, we do about 40 schools a year!
 
Re: Is there any difference in inspecting and testing a school, to a domestic install

What ya messin at!!!!!!!!!
Get stuck in. Just have your wits about ya and think what ure do'in.
 
Re: Is there any difference in inspecting and testing a school, to a domestic install

Pay consideration to the change in external influences as well.
 
Re: Is there any difference in inspecting and testing a school, to a domestic install

Phase balancing , loading , also wiring methods clipped direct how the cables are protected , seen a school where the cables were clipped direct down a wall it was full of holes due to a bored pupil and a compass , and i know its petty but make sure you check every socket for the shutters are working you'd be suprised whats stuck in the things , also positioning of consumer units , placing out of reach ,as widdler has said too , the testing is very much the same just normally three phase , but but rigorouse with the visual side
 
Re: Is there any difference in inspecting and testing a school, to a domestic install

Don’t be too surprised if you can’t get any readings from the sockets in the science labs. They are usually supplied via “Blackley Units (Transformers with RCD’s & MCB’s)”. Also, make sure the isolators and emergency stops are functional in the workshops.
 
Re: Is there any difference in inspecting and testing a school, to a domestic install

Don’t be too surprised if you can’t get any readings from the sockets in the science labs. They are usually supplied via “Blackley Units (Transformers with RCD’s & MCB’s)”. Also, make sure the isolators and emergency stops are functional in the workshops.

kamikaze are you feeling ok mate? It's the first time in 838 posts that you've talked about electrics ;););). (i know you'll get your own back :). )
 
Re: Is there any difference in inspecting and testing a school, to a domestic install

kamikaze are you feeling ok mate? It's the first time in 838 posts that you've talked about electrics ;););). (i know you'll get your own back :). )

Rumour has it I was in a state of altered consciousness. The truth however is I can’t think of anymore mindless nonsense. Besides, I have to get cracking if I want to keep up with that post-ho Telectrix.…lol ;)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Is there any difference in inspecting and testing a school, to a domestic install?