So the incoming power is coming from X1 and three phase is being distributed to Q1 using 25mm cable. Phase 1 & Neutral are going to Q2. I was curious as to what cable size is acceptable going to Q2? I assumed it would also need to be 25mm but I've been told as its pulling a maximum of 1A that 1mm is acceptable.
Is this correct or is this a safety hazard?
Thanks in advance, first time post and new to the industry.
 
The pfcc and pscc on a circuit run in 1 mm is going to be a lot lower than is required to break the incoming.
So no 1 mm won’t do it.

Edit : having read robs post. If there is a very low chance of a fault occurring then yes I may agree with him, but it’s not something I’d do.
 
Edit : having read robs post. If there is a very low chance of a fault occurring then yes I may agree with him, but it’s not something I’d do.

It's within a control panel, it's very common to see this and also panel lights, maintenance sockets and BMS supplies fed off the incoming side of the panel isolator. All marked, live when panel isolator is off.
 
The pfcc and pscc on a circuit run in 1 mm is going to be a lot lower than is required to break the incoming.
So no 1 mm won’t do it.

Edit : having read robs post. If there is a very low chance of a fault occurring then yes I may agree with him, but it’s not something I’d do.

It's a common method of doing things in control wiring.

However the stipulation is the wire length (<3m) and it hasn't to be likely damaged, so realistically, inside trunking within a control panel it's not.
 
View attachment 51295
So the incoming power is coming from X1 and three phase is being distributed to Q1 using 25mm cable. Phase 1 & Neutral are going to Q2. I was curious as to what cable size is acceptable going to Q2? I assumed it would also need to be 25mm but I've been told as its pulling a maximum of 1A that 1mm is acceptable.
Is this correct or is this a safety hazard?
Thanks in advance, first time post and new to the industry.
View attachment 51295
So the incoming power is coming from X1 and three phase is being distributed to Q1 using 25mm cable. Phase 1 & Neutral are going to Q2. I was curious as to what cable size is acceptable going to Q2? I assumed it would also need to be 25mm but I've been told as its pulling a maximum of 1A that 1mm is acceptable.
Is this correct or is this a safety hazard?
Thanks in advance, first time post and new to the industry.
The apprentice from what I’m seeing is the arrow you drew was pointing at the grounding conductor and after 30 amps you can defrayed the equipment ground. Looks fine to me
 
Although it is fine to do that as discussed above.
I prefer to size cable in that scenario bigger than required.
I think I would have used 4mm, apart from any other reason, it tends to fit the larger terminals found in the isolator a bit better.
 

Reply to Is this acceptable? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top