Not all inverters need RCD protection, however, there should be an isolation switch at an accessible point, the loft is not an accessible point.
 
I can't believe they haven't used two AC isolators - one near the inverter and one at the house.

Why are there cables in the loft or is that a different job entirely?

Is the long cable buried? How deep?
 
The loft cables are nothing to do with the Solar PV.

Yes the supply cable is buried but according to the client only about 150mm deep !

I will keep you informed re any further info.

Thanks again.
 
I can't believe 150mm is deep enough! Is it running down the garden? It should be at least 600mm with a yellow "cable below" warning tape halfway down.
 
I can't believe 150mm is deep enough! Is it running down the garden? It should be at least 600mm with a yellow "cable below" warning tape halfway down.

Carefull - before you start specifying minimum depths.

BGB says 'should be at a a sufficient depth to avoid being damaged by any reasonably foreseeable disturbance of the ground' - the only place where the regs specifies minimum depths is agricultural, camp sites and marinas.

If buried at a depth of 150mm then whoever did it needs to have a good explanation to say why 150mm is sufficient.
 
I can't believe 150mm is deep enough! Is it running down the garden? It should be at least 600mm with a yellow "cable below" warning tape halfway down.

The 600mm is only a recommendation. It's up to the designer to assess the depth of the buried cable. If its not considered to be on agricultural land I.e. a crop field or passing under a vegetable patch ect then bury it as the designer chooses. Mind you can never tell what tomorrow brings so 600mm is always a good recommendation :D
 
Carefull - before you start specifying minimum depths.

BGB says 'should be at a a sufficient depth to avoid being damaged by any reasonably foreseeable disturbance of the ground' - the only place where the regs specifies minimum depths is agricultural, camp sites and marinas.

If buried at a depth of 150mm then whoever did it needs to have a good explanation to say why 150mm is sufficient.

Beaten to it :D
 