What is the Ra of the TT system, or Ze if you have checked it that way?

Not that it matters too much at the moment because the new circuit is non-compliant due to the undersized cable.
Just checked the Ze of the electrode. It’s 152ohm. Will close this thread for the mean time as I realise the wrong cable was selected. Fortunately it’s at my parents house so it doesn’t have to be exactly ‘to the regs’. I’m used to an industrial setting with 3-phase so it’s a different ball game. I’ll update when I sort it out and recalculate max demand etc. Thanks all for your help
 
Just checked the Ze of the electrode. It’s 152ohm. Will close this thread for the mean time as I realise the wrong cable was selected. Fortunately it’s at my parents house so it doesn’t have to be exactly ‘to the regs’. I’m used to an industrial setting with 3-phase so it’s a different ball game. I’ll update when I sort it out and recalculate max demand etc. Thanks all for your help

It does have to comply with the regulations, and personally I would consider this to be even more important when it is my own family who could be put at risk from non-compliances.

Cable calculations are exactly the same ball game whether it's industrial or agricultural, the only real difference is the additional rules for agricultural as its a special location.
I assume its agricultural as its has a shepherds hut and that implies a farm.
 
Have you got an rcd of some description upfront on the cable for fault protection as its TT?
 
Did you bury the swa, maybe you could just run a parallel cable with it????

That means digging it all up again if it's buried, so might as well go with one replacement cable as damage to the original is pretty likely.

Plus they'd need a total of 3x 2.5mm to get an acceptable voltage drop for a socket circuit, not really a sensible soloution
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Yorkshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Is this OK? 100m run of SWA
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
scoul00,
Last reply from
ChrisElectrical88,
Replies
21
Views
3,968

Advert

Back
Top