phyllism
USA
I have an oil burner with baseboard heating and the air handler (which has the c wire run to the thermostat) connected to the ATS for the generator. AC is not connected to the generator. What happens when power is lost during heat mode?
Does this cause a load problem on the generator?
Reply to Is this wiring ATS for generator? in the DIY Electrical Advice area at ElectriciansForums.net
Even if it’s says that the neutral is bonded to the generator, you still are required to install a ground wire from the generator to the transfer...
It will pull 21.4 amps which is an actual load and the breaker is sized based on the calculated load. Which is 30 amps