a domestic electrician was employed by the contractor to install extra emergency lights to existing lighting circuit within a plant room
the existing lighting circuit is wired in 1.5mm FP200 cable and fixed to cable tray for suspended ceiling and wall lights
the electrician used 1.5mm flexible cable tapping off from existing emergency lights
the longest run is 6 metres
the electrician claimed the flex is heat resistant and therefore acceptable

is he correct ?
 
It sounds as though it's electrically safe. In terms of being correct or incorrect from the info provided here there's nothing to immediately suggest it wouldn't pass a periodic inspection.
Let's turn the question around: What is it about the environment that necessitates using FP200 for emergency lighting?
 
It sounds as though it's electrically safe. In terms of being correct or incorrect from the info provided here there's nothing to immediately suggest it wouldn't pass a periodic inspection.
Let's turn the question around: What is it about the environment that necessitates using FP200 for emergency lighting?
the plant room is in a commercial building, it contains 2x MCCP's, 3x boilers, LTHW & CHW pump sets, 3x PU's and 2x calorifiers, existing wiring is either enclosed within metal trunking or conduit, only the lighting circuit is wired in FP

could the electrician have used Twin & Earth instead
could the plant room be wired entirely in Twin & Earth
 
a domestic electrician was employed by the contractor to install extra emergency lights to existing lighting circuit within a plant room
the existing lighting circuit is wired in 1.5mm FP200 cable and fixed to cable tray for suspended ceiling and wall lights
the electrician used 1.5mm flexible cable tapping off from existing emergency lights
the longest run is 6 metres
the electrician claimed the flex is heat resistant and therefore acceptable

is he correct ?
It normally is dependant of the specifications of the install if the design/architect specifies a certain type of wiring then that’s what us electricians install. Without going to my van and getting my blue bible out I’m not 100% sure on the thermal characteristics are of each cable type but sounds like you are not happy with the install so you need to provide evidence for your reasoning I don’t think there is anything wrong with the install unless it’s not in accordance to the design spec
 
According to my "Electricians Guide to Emergency Lighting"

"Self-contained emergency luminaires do not require fire-protected cable supplies."

It then says that the wiring to self-contained emergency luminaires is actually recommended to be the same as the normal lighting, because of certain 'unusual circumstances' where they may not operate when needed. (not well explained, but I think the case of a fire causing failure of supply to normal luminaires but not the emergency ones and that stopping them detecting the loss of power and thus not operating correctly)

Central supply installations are a different kettle of fish and have to meet BS7671 Chapter 56 (so would need fire protected cables)

There's a separate issue here though of it being a plant room with very different environment to a domestic one, so not sure if that would affect the cable chosen...
 
As an Amazon Associate Electricians Forums may earn a small commission from qualifying purchases.

Reply to is wiring correct or incorrect in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
446
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
680
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top