Hi

Weird problem.

I’m replacing plug sockets. I isolate the circuit for the particular sockets at the fuse board so it is safe to swap out. All good. Suddenly the RCCB for all sockets - not just the circuit of the sockets I have isolated - trips. Why is this happening?

The RCCB doesn’t trip when all the circuits are live. It is as if it won’t let me isolate an individual circuit as it trips the whole consumer unit shortly after I isolate a circuit

Thanks
 
If by “isolate the circuit” you mean that you turned off the MCB then you have not isolated the circuit fully. The MCB only turn off the line.
To fully isolate a circuit you need to disconnect the neutral as well.

The RCBO/RCD may trip if the neutral is still connected and you touch a neutral conductor to earth.
 
If by “isolate the circuit” you mean that you turned off the MCB then you have not isolated the circuit fully. The MCB only turn off the line.
To fully isolate a circuit you need to disconnect the neutral as well.

The RCBO/RCD may trip if the neutral is still connected and you touch a neutral conductor to earth.
Oh maybe that is it - I flicked the MCB - so you are saying that an earth and the neutral touched? Thanks
 
How do I disconnect the neutral after turning off the MCB?
It would be dangerous to try unless you've had plenty of practise. Please don't try and do this.

Just change the sockets under daylight hours, isolate the circuit as you did (or better just use the main switch), and try and avoid touching the wires together. When changing sockets it shouldn't be too hard to keep them separate.

The reason is that the Neutral wire is connected to other Neutral wires and touching it to earth is providing an alternative path back for some current, so the safety device kicks in just in case this current is going through a person.
 
It would be dangerous to try unless you've had plenty of practise. Please don't try and do this.

Just change the sockets under daylight hours, isolate the circuit as you did (or better just use the main switch), and try and avoid touching the wires together. When changing sockets it shouldn't be too hard to keep them separate.

The reason is that the Neutral wire is connected to other Neutral wires and touching it to earth is providing an alternative path back for some current, so the safety device kicks in just in case this current is going through a person.
Thank you - appreciate the advice
 
Just to add that you should be using the main switch to isolate rather than a circuit breaker, as it is not considered isolation for the purposes of a single phase domestic property for an unskilled person unless all live conductors (which includes the neutral conductor) are disconnected.
 
You are most welcome.

Stupid rule.
Just to add that you should be using the main switch to isolate rather than a circuit breaker, as it is not considered isolation for the purposes of a single phase domestic property for an unskilled person unless all live conductors (which includes the neutral conductor) are disconnected.
So is it dangerous to work on a circuit when I use the circuit breaker? I always check with a non-contact voltage tester there is no voltage on the circuit before commencing work on that circuit. Turning off the main switch seems a bit over the top just to work on one circuit? Plus I need lighting. Thanks for your thoughts.
 

Reply to Isolate circuit but trips fuse board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

For a TN system neutral is deemed at earth potential.
Replies
6
Views
375
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
387

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top