Issues with megger mft1720 | on ElectriciansForums
Discuss Issues with megger mft1720 in the Electrical Tools and Products area at ElectriciansForums.net
Hi
I've got a megger mft 1720 that I was hoping any one can shed any light on
When performing continuity tests (even when nulling the leads) and earth loop tests I seem to get higher readings than normal.
After a while of testing the tester seems to settle down and gives more accurate readings.
The tester has been calibrated a few months ago but has been like it for a while now. I've also brought a new set of leads in case they was the issue but still the same problem.
Has any one had any simular issues with their megger?
I've had it a few years now and purchased it second hand so unsure how old it actually is. Even when nulling the leads I get something like .40 but never the same reading it fluctuates then eventually calms down to around .20 when been used for abit
Try a new set of leads.
The sockets the test leads plug into are actually themselves connected to plugs which plug into the motherboard.
I'd suggest giving them a clean:
Remove these two screws:
[ElectriciansForums.net] Issues with megger mft1720
And prise the socket block out using a screwdriver as shown.
Clean up the contacts both on the sockets:
and inside:
You can also try shorting out the red and green motherboard sockets to check for consistent repeatable results, ruling out the socket block, leads, clips etc.
That will tell you if it's the tester itself or not.
If the leads are giving 0.4 or even -.2 that's higher than they should read. I'd expect about 0.1. Suggests that it needs to go back to get looked at by the calibration place if you've tried a new set of leads. Unless you try the above and it works
If you have calibrated it should be OK
Send it back,.
I have a 1720, few years ago it had been calibrated by a company and it came back ok ,next thing i was not getting loop testing ,sent it to the collaboration center Manchester .
I actually don't think this one is a calibration issue per se as the readings improve with time.
I think it's either poor contacts as per above or a failure on the measurement PCB.
But either way a decent calibration center should sort this.
If it's 1st generation PCBs then all 3 PCBs would need changing and it's cheaper to send it to Megger, as for a fixed repair fee ~ ÂŁ250 it will basically become a 1721 and gain 2 wire lo-current loop tests (though I'd never actually trust the results of these!)
But first things first - I should clean the socket block first and then short out and use known resistances directly on the PCB contacts to see if you get consistent results.
Hi guys
Quick update. Took the terminal block out tried a few resistors straight across the motherboard and was getting pretty consistent results. Put the block back in and the testers seems a lot better and more consistent readings. When nulling leads its around 0.17ish and doesn't fluctuate like it did before.
Still thinking about upgrading to a new tester and thinking of sticking with megger as i find them very easy to use with quick rcd tests.
Quick question how do you guys get around rcd uplift when doing earth loops? i do quick a few EICR's and find myself doing both dead tests and live tests just because the live tests aren't true readings due to RCD uplift.
Well done. Leads sound a bit high btw mine are 0.07 when warmed up.
Rcd uplift - I either calculate Zs, or use the kitcher trick.
See
and inside:
Hi Tim
Do you know if the socket blocks are available as spare parts? I've got a pin snapped off in mine and I can't get it out!!
Cheers in advance
Reply to Issues with megger mft1720 in the Electrical Tools and Products area at ElectriciansForums.net
There is a lock on it, press the test button down and press the lock button, the symbol will appear on the screen in the middle right hand side...
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
