Sounds like its a TN-S m8, I would carry out an IR test on the installation as well, you dont need to mention the fact there is no PME, you have said it is earthed to the supply sheath, so as above it makes it a TN-S. Have you taken a ze?
 
Brilliant guys thanks! so a test certifiate can be issued? :D

All i shall note in the recommendations like you say is:

"No Earthing on lighting ciruit therfor not suitable for class 2 equipment and unable to obtain readings for this circuit".

Anything else you wud recommend putting down guys? All the equipment used on the circuit is the original from the original installation anyway. No new pendants or switches or anything!


No earthing on lighting will mean it is unsuitable for Class 1 equipment.
Any mention on presence of RCD's?

It would be ideal in the situation of no cpc's to then carry out an IR test between line and neutral, just to spot any evidence of degrading, which is likely for an installation of this age.


Have you observed best practice guide 4? May be helpfull??

http://www.esc.org.uk/pdfs/business-and-community/electrical-industry/BPG4_08.pdf
 
I (or you) may be missing the point here.:)

The certificate you issue will be a Periodic Inspection Report. From what you have said the installation will fail the inspection badly on a number of serious issues. No loan company in their right mind will let your customers borrow any money against their home with the installation in the state it is.

Your course of action would be to carry out a PIR, to ascertain exactly how bad it is....(sounds re-wire bad to me) then carry out all necessary remedial works, and then issue an EIC stating that all the remedial works have been carried out and certifying the work you have carried out and that the house is now in a safer condition.:)
 

Reply to Issuing a Test Certificate...... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
778
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

On the minor works in the brown book it has Zdb
Replies
3
Views
283
They have done electrical work... they should test it before anyone else gets a chance to alter it. In fact... here it is from the BBB "641.1...
    • Like
Replies
3
Views
534

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top