I had an emergency call out to replace a consumer unit, (used a fully 18th edition compliant board) when compiling the installation certificate your not allowed any limitations.

now i know the rest of the house does not need to conform to 18th edition standards but The house is a large house so asides from anything obviously non compliant highlighted in my testing am i expected to ensure 100% of the installation is con formative because i cant with cables being in floors wall and partitions, i also certainly wont be dropping every accessory.

Where do i stand on this?
 
You are not required to make sure the installation in the rest of house is compliant, if you were every board swap would be a rewire for me.

You are required to ensure that all connected and energised circuits are safe. Your testing and cert will demonstrate this.

I suggest you download and read through best practice guide 1, it will help clear a lot of issues up.
 
100a main switch, as i am sure you are aware SPD AFD are only a required recommendation unless you can see the need for them in a domestic
100A main switch has been common for consumer units for many years.

Here's the link for the best practice guides
Best Practice Guides | Electrical Safety First - https://www.----------------------------/professional-resources/best-practice-guides/
 
You can’t have limitations on the board

As in you can’t ommit rcd protection for example

The remainder of the house wiring is irrelevant so long as it’s safe for continued use

If it wasn’t safe you probably wouldn’t be changing the board in the first place
 

Reply to Issuing and installation certificate in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top