As others have said, most likely hospital operating theatres or intensive care units or other 'life support' systems.

The reason for this are because it is 'first fault' tolerant, it needs at least two simultaneous faults before it will trip or disconnect.

It is forbidden to be used for public supplies (at least in the UK), and is fault monitored and used under supervision.
 
Yes, Hospital operating theatres and some other medical rooms will use IT earthing systems.

In Operating theatres it will be a fully monitored IT earthing system, along with differentiation/separation of earthing connections. ..ie PA and PE. PE being electrical earths, and PA building and other earthing points. Both connected to there own earth bar at the supplying DB, connected/linked by a 16mm removable connection link.


Much more too it than that mind...lol!!! The new section in BS7671 on Medical Rooms, is almost a direct take off of VDE/DIN 0100/007... (i think that's the right vde/din number anyway..lol)
 
spark 68,
You will have earth fault monitoring & warning, but it is doubtful that you will have much disconnection of supply in the event of an, or possibly multiple earth fault (s) as this could kill someone! ;)

It depends a lot on the designer and other things within the design to provide protection, no a "simple" solution like much of 7671 pretends to be.
 

Reply to It system where? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
851

Similar threads

N
  • Article
Where to put softener in water system? I live in Azerbaijan, the house has three full bathrooms and has had up to 7 people living there. We store...
Replies
0
Views
135
naylorpd
N
Yes sir. Exactly that. Probably got about 8 individual switch lines. I could bunch to slim it to 6 if needed
Replies
2
Views
349

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top