It weren't broke until I got there an' improved it. | on ElectriciansForums
Discuss It weren't broke until I got there an' improved it. in the UK Electrical Forum area at ElectriciansForums.net
Marti
Poole, Dorset
So...
This is all on my house and no animals were harmed in the making of this hash up but the Mrs doesn't know...yet.
A few years ago we had this house rewired. Usual story, a lash up by an unqualified because we knew no better and it was one of the incentives for me to qualify and offer a better service.
The CCU is an amendment 3, 16 way, split board rats nest but I've completed an EICR, resolved the issues and all was well. Trouble was I hated the rats nest and gave an afternoon to stripping it out, labelling, making sure the L and N were each in the correct side of the board, all tidy and collecting my gold star.
I have a garage CCU running via 40a type C via SWA to my workshop. One RFC and a light via an RCD.
NOW if I plug in any device in the workshop the 40a type C (at the house) trips with the relevant RCD. IR, polarity and RCD all test fine at the workshop so I've buggered something at the house end. Does this mean I should have been a plumber / pimp / Trump supporter?
Apologies for the long story. I have humour where my dignity should be. What are your thoughts on the problem
two rcd in series not good .
So...
Have you taken the feed for the W/Shop from an MCB and taken the N from the wrong N busbar? without being there it's very difficult to trace any faults, maybe a borrowed N causing your problems, either that or you have screwed up the connections at the W/S CU.
Thanks Guys,
My bet, from what you've said, is that I've got the neutral in the wrong bar. Haven't had time to check but I'm confident that, from the SWA onward is fine. Funny enough, this was the situation that prompted me to asked about labelling in another thread.
That correct SC. the fact that this was working perfectly until I fixed it suggested the issue is at the house end where I tidied up the wiring but double checking all the workshop installation did seem good practise.
Does the same occur if you turn the lights on in the workshop?
Reply to It weren't broke until I got there an' improved it. in the UK Electrical Forum area at ElectriciansForums.net
What I find a little bit interesting is that there was an era of MFT's e.g. Robin, early Kewtech that tried to do non-trip loop tests using D-Lok...
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...