Good question! I was taught that you had to add a protective device whenever the csa was reduced. This is I think application of 434.2. However it does look you are correct according to the exception in 434.2.2 which treats a change in csa the same as a change in installation method etc. i.e. select the PD for the circuit based on its minimum capability.What's all this about adding a fuse?
If the protection at the origin of the circuit is rated for the smaller cable, no need to stick an additional fuse in where the cable sizes change.
For example, you might choose to do a long lighting run in 2.5mm² to minimise voltage drop and then do the final few metres to fittings in 1mm² or 1.5mm² to make termination easy. If it's all on a 6A breaker, no problem.