What's all this about adding a fuse?

If the protection at the origin of the circuit is rated for the smaller cable, no need to stick an additional fuse in where the cable sizes change.

For example, you might choose to do a long lighting run in 2.5mm² to minimise voltage drop and then do the final few metres to fittings in 1mm² or 1.5mm² to make termination easy. If it's all on a 6A breaker, no problem.
Good question! I was taught that you had to add a protective device whenever the csa was reduced. This is I think application of 434.2. However it does look you are correct according to the exception in 434.2.2 which treats a change in csa the same as a change in installation method etc. i.e. select the PD for the circuit based on its minimum capability.
 
No not quite Br there is nothing wrong with say having a 10mm cable with a 45amp PD and the last 2 metres in 4/6mm say, providing you can achieve all the criteria of the regulation

sorry, i am not sure I follow you. 4mm would not be protected by the 45A PD so how is that allowed?
From my re-read of the regs I thought that would only be allowed if the PD is smaller than the current rating of the 4mm.

Do I need to read the regs again? :(
 
Last edited by a moderator:
Yes remember we have 2 conditions concerning protection over current and fault protection

Have a look at 433.3.1 and section (i) particularly about and a device need not be provided

You are right, I referenced the regs on fault protection when I was talking about current capacity and overload protection. But doesn't 433.3.1 affectively say the same thing? i.e. a supply side PD must be capable of protecting the cable under fault (434.2) and overload (433.3.1).

I know there are always exceptions (eg 433.3.1 (ii)) but in general it still appears to be saying the PD must be selected for the minimum capacity of the circuit.

If I have still got it wrong you might have to spell it out for me.... :(
 
I think blue crimps are rated from 1.5 to 2.5 if u look on the packet

not if using proper crimps with an approved crimp tool(ratchet type) which was brought in to ensure a correct crimp regardless of the strength of the individual,as ratchet does not release until crimped to a predetermind level,in fact crimp tool manufacturers(biccon)recommend you only use the crimp made by the crimp tool manufacturer as there can be differences in size between makers,I have seen this when using cheap crimps and sometimes they will pull out,ex father in law used to work at biccon in r&d so thats how I know so much about them.
 
IMHO a Wago is great if it's enclosed and accessible. The beauty of a crimp is that you can shrinkwrap it and hide it.
526.3 (vi) allows maintenance free but none of the Wagos I have have "MF" embossed on them. Do they conform to BS5733? They also all have a "test" hole which means they are not to IP4X (and so need an enclosure).

Laurie
 

Reply to joining cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Blue? You haven't joined it completely back together! The copper screen around the wires needs to be continuous, ie you need to connect the two...
Replies
1
Views
231
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
513

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top