Did any of you sit it? I didn't think it was TOO bad, couple of questions I was a little unsure of but overall ok. How did you guys find it? I can never think of the bloddy questions afterwards!
Polarity all switches fuses and single pole devices connected in the line conductor only- ensure centre contact of Edison screw lampolders connected in the line conductor only exception e14 and e27 - ensure all sockets and accessories are connected correctly
Upvote 0
Polarity all switches fuses and single pole devices connected in the line conductor only- ensure centre contact of Edison screw lampolders connected in the line conductor only exception e14 and e27 - ensure all sockets and accessories are connected correctly[/QUOTE
Did you answr the question on the containment system? Was this referring to the check list in GN3 on trunking and conduit.
Upvote 0
discribe what you would check for on the pvc conduit and trunking
discribe 4 items to check for on the armoured installation useing the sense of touch
discribe the insulation resistance value effects on between live conductors on a switched sput containing neon lamp switched in the off position
explain why the dno cant give values on a tt system
what earthing arrangment applies to external earth fault values of 0.35,0.8,21 ohms
cant think of anymore
What inspection is to be carried out on a severely over loaded installation
What areas would you be most concerned with during the inspection.
Upvote 0
I answered check properly fixed using sence of touch ( give it a shake ) ensure all lids are in place visual inspection correct position and number of boxes for easy draw of cables visual inspection not sure if that was the Answers they where looking for but thats what they got lol
Upvote 0
As many are talking about the volt drop question the correct answers were: 3% for lighting from a public distribution system (so 6.9V of 230V), 8% for the 3 phase motor supplied from a (private) factory generator (so 32V of 400V, I think it was 400V), 5% for the immersion heater in a domestic home (supplied from a public distribution system so 11.5V of 230V). I think I remember these in order. Percentages for volt drop can be found in appendix 12 of BS76 71 Table 12A
What made you think it was supplied by a private generator?
Upvote 0
i put check ends are bushed and reamed , radii of bends for conduit. protected against mech. damage. securely fixed.
IR i answered 'no effect'
earthings arrangement i said tn-c-s , tn-s and tt
what do you think is that right ?
Upvote 0
in regard to the question 'what two test currents on a 100mA RCD' i answered 1x and 5x ... well just looked at my tester (fluke 1653) and set to 100mA . doesnt give an option to test at 5x so that answers that one . thing is though, when i select 1000mA RCD , i can test that at 1/2x or 1x !!!
Upvote 0
I might be wrong but dont you only need to do the 5 times test when you are testing a rcd/rcbo giving additional protection .so I delta N value of less than or equal to 30 ma ..