A BS1361 fuse is to be used to provide overcurrent and fault protection for a new circuit. State the effect on the operation of the fuse when the following conditions occur if the fuse was installed in the neutral conductor:

a) Overload

b) Earth Fault

c) Short circuit fault


Let the discussion begin :):):)
 
A BS1361 fuse is to be used to provide overcurrent and fault protection for a new circuit. State the effect on the operation of the fuse when the following conditions occur if the fuse was installed in the neutral conductor:

a) Overload

b) Earth Fault

c) Short circuit fault


Let the discussion begin :):):)

I put

a break
b none
c break
 
Last edited by a moderator:
A BS1361 fuse is to be used to provide overcurrent and fault protection for a new circuit. State the effect on the operation of the fuse when the following conditions occur if the fuse was installed in the neutral conductor:

a) Overload

b) Earth Fault

c) Short circuit fault


Let the discussion begin :):):)

I put;

a) Trip
b) No trip
c) Trip

Will i find out if i'm totally wrong???

I need to have bagged as many as i answered as i ran out of time whilst answering 25!:eek:
 
I think they're looking for example:

The fuse operates (opens) or the fuse does not operate.

But I'd like to think that using the word trip would not affect the awarding of marks!
 
Last edited by a moderator:
I used a different variation....

a) fuse element breaks
b) no effect
c) element breaks

How many more versions did folks but i wonder?Lol

Seems as we all had the same idea at least, hopefully we've bagged the 3 on that one, only need another 87 from the others!!!:eek:
 
I waffled loads on this one. The question asks about the effect on the fuse, but I thought it was about the effect on the whole circuit.
a) The fuse blows, but the whole circuit is still connected to line voltage. With no current now flowing, all parts of the circuit - including the neutral conductor, are 230v above earth.
b) The fault current flows through the CPC, and not the neutral conductor. The fuse will not open and the circuit is not protected.
c) Same as a)

Wasted some useful minutes on that one.:cool:
 
They will be happy with that Charles... You showed underpinning knowledge, but wasted a little time tho i think.

As the exam success says, the word state means use as few words as is necasary.
 

Reply to June 2391 Question 15 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
Some of the points should have been picked up by previous people doing the testing. Sounds like this is a thorough report. Not everything is...
Replies
11
Views
2K
The cable needs protecting the same as if a load was connected on the far end of it, rather than a generator, except that it must not share a RCD...
Replies
7
Views
2K
For most domestic work the "standard circuits" in the On-Site Guide Table 7.1(ii) are all pre-checked for adequacy in these aspects, also there is...
Replies
3
Views
1K
In years gone by many of us would feed an additional small CU [say for a shower or outbuilding for example] with 6mm tails, often directly...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks