just want to check if this is correct | on ElectriciansForums
Discuss just want to check if this is correct in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
B
bobby101
testing on the 2391 insulation resistance test rig
for three phase
isolate cb supplying s/p board
Check meter, test DB is not live
disconnect neutral
test between lines neutral and earth
test between lines and neural A repeat of above?
test between lines
reconnect neutral
for single phase
isolate rcd main isolator
link line busbar to neutral busbar
test between line and earth
ensuring strappers are brought into test
disconnect link
isolate dimmer circuit
test between line and neural
I have made a comment on your OP in red.
One question: Why disconnect anything? testing should not interfere with the integrity of the installation. (IMHO) My (1999) 2391 did not involve disconnecting within the DB, only installing a link on a spare way for R1+R2 etc.
Reply to just want to check if this is correct in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...