Prestatyn
hi whilst testing ELI on lighting circuits, using kewtech kt63 on loop no trip function, test keeps tripping rcd once polarity and voltage is confirmed. I know the kt63 tests at 250v in this mode, but it shouldn’t trip the rcd, anyone else experienced this? Is it calibration time? Is it me? Is it the rcd? Anyone’s thoughts, and I know the calculation is Zs =(Ze + r1r2), a bit frustrated the damn things keep tripping, upstairs and downstairs, separate circuits, separate rcds, both trip.
Watch the R1R2 thing r1,rn and r2 are endto end readings of a ring final circuit
Zs= Ze+(R1+R2) your formula is wrong
Hi - did you unplug everything and turn off lights from the final circuits supervised by the RCD ? (as there may be loads with leakage)
Yeah even down to disconnecting separate cooker hood circuit from mcb. Needed doing anyway to do fused switch change and test, so not a hassle but still same result, all light bulbs removed everything.