izzy76

hi
i got a 3ph 500amp distribution box with 8 63amp3ph isolators feeding other different sub distributions, i need to install a sub kilowatt hour meter on just 3 isolators feeders but dont wish to modify the main distribution .... can i clamp each phase with different current transformers and wire them so they feed a single 3ph 250amp kilowatt hour meter.... is it possible to wire the cts in a way so i can monitor the consumption (in parallel or in series) one ct for every phase respectively ...
i hope i was clear enough
thanks in advance
 
izzy, Have you got a Main fused switch feeding a busbar chamber & then the 8 x3ph 63A switch fuses or a panel board with a main MCCB & 8x63A MCCB's. If the latter you may be able to install the CT's[ current transformers] within the common wireway [ ensuring the signal cable terminations are shrouded]. Then fit the meters on the top of the panel.[ all depends on access/ layout etc, this is one suggestion]
If you have a busbar chamber & seperate switch fuses, you may have to route the supplies to these [ or the 3 you wish to monitor] via an enclosure [ for the CT,s.] or in either case use direct reading check meters. I have presumed the3 phase isolators / switch fuses / MCCB's are feeding 3 phase boards & not 3 single phase boards [ which is bad practice for isolation]. Further info may give better idea of layout / distribution. piccollo
 
hi piccollo ... yes i got a fused incomer feeding a busbar chamber , the 8 isolators are feeding 3phase dbs .... the 3 feeders i wish to monitor are feeding a part of the establishment, now the problem is that it is not possible to install a kilowatt meter for every feeder cause of space and budget, if each of the phases example the brown phase of each feeder is passed through the concerned ct will it read the total amount of current passing through the 3 different feeds? one ct with 3 brown cables passing through it , same is done on the black and on the gray... will the cts sum up the current flowing?
thanks for ur interest and help
 
izzy, yes you can use one meter. Suggest insulated enclosure [ mounted on or near bus bar chamber with insulated studs/ short bars to house CT's & local 6amp fuses / 3 phase 6 amp mcb] renew tails [ unless you can easily get them through CT aperture], you will know what space you have, then local fuses can be fed off of the stud [ min 6mm2] or one of the isolators. I don't like putting CT's in a busbar chamber as generally not a lot of spare room. piccollo
 

Reply to kilowatt hour meter in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
245
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top