S

Snapester

Designing a kitchen appliance circuit, i plan to feed a bank of grid switches with a 6mm T&E fed via a 32A MCB, then each switch will have a 2.5mm cable to a fcu supplying an under counter appliance.
My main question is, is it ok to change down to 2.5mm and then feeding the FCU? As the cable cannot be overloaded as the main load is connected to the FCU at position?

Regards
 
It seems a little strange running two ring legs from the CU straight to the grid plate? Surely 1x 6mm will be exactly the same? I fail to see the difference apart from conductor size?
 
I gather the whole idea that the switch supplies x amount of points but why run 2x 2.5mm 20m to the grid whereas 1x 6mm will be more than adequate?
 
It seems a little strange running two ring legs from the CU straight to the grid plate? Surely 1x 6mm will be exactly the same? I fail to see the difference apart from conductor size?

Do 2 installations,one with a 6,0mm radial supply and another with 2,5mm ring.fit the grids then decide which was the easiest and better quality arrangement
 
Well according to Mk Data sheet 2x6mm is possible! Although i think looping with 4mm will be a better option and just having main feed as 6mm.
 
You have had many opinions, so all I can now say is, everyone to their own ways, hope it works out for you

I will think of this thread the next time I'm putting those little loops across the grid switches
icon12.png
 
What about in the event of a short circuit at the FCU?

Edit: Or a fault at the FCU that somehow results in 32A and no more being drawn through the 2.5mm cable?

Fire hazard me thinks

OK - I'm not tring to be contentious here - I'm sure you are more experienced than me; but are you saying that my reply is incorrect? I was thinking say for example on a 32a radial in 4mm T&E. You are permitted to spur off to one double socket in just 2.5mm T&E. We are not suggesting that 2.5mm will be ok at 32a.
Happy to be corrected so long as it's constructive.
 

Reply to the thread, titled "Kitchen Appliance circuit" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top