Designing a kitchen appliance circuit, i plan to feed a bank of grid switches with a 6mm T&E fed via a 32A MCB, then each switch will have a 2.5mm cable to a fcu supplying an under counter appliance.
My main question is, is it ok to change down to 2.5mm and then feeding the FCU? As the cable cannot be overloaded as the main load is connected to the FCU at position?

Regards
 
There was an article in NICEIC mag about putting grid switches on ring and how it needs to be balanced at the middle of the ring, i will see if i can dig it out! Also the grid switch is one point so i wouldn't want to run a ring to one point?

Why not ?

If the grid assembly is the only outlet on that circuit,the ring will be almost perfectly balanced

I would say keep it simple 2,5mm ring to the grid assembly on its own 32A mcb,
If you want ,you can fit grid fuses as well for the loads and outlet plates for the appliances

I would also suggest the 20 amp rating refers to the switch contacts not the supply terminals
 
Last edited:
It seems a little strange running two ring legs from the CU straight to the grid plate? Surely 1x 6mm will be exactly the same? I fail to see the difference apart from conductor size?

Do 2 installations,one with a 6,0mm radial supply and another with 2,5mm ring.fit the grids then decide which was the easiest and better quality arrangement
 
You have had many opinions, so all I can now say is, everyone to their own ways, hope it works out for you

I will think of this thread the next time I'm putting those little loops across the grid switches
[ElectriciansForums.net] Kitchen Appliance circuit
 
What about in the event of a short circuit at the FCU?

Edit: Or a fault at the FCU that somehow results in 32A and no more being drawn through the 2.5mm cable?

Fire hazard me thinks

OK - I'm not tring to be contentious here - I'm sure you are more experienced than me; but are you saying that my reply is incorrect? I was thinking say for example on a 32a radial in 4mm T&E. You are permitted to spur off to one double socket in just 2.5mm T&E. We are not suggesting that 2.5mm will be ok at 32a.
Happy to be corrected so long as it's constructive.
 
So in essence the radial basically has many 2.5mm spurs! And i wouldn't need FCU i could just use unswitched socket outlets.
Wow learn something everyday on here!
 
Last edited by a moderator:
OK - I'm not tring to be contentious here - I'm sure you are more experienced than me; but are you saying that my reply is incorrect? I was thinking say for example on a 32a radial in 4mm T&E. You are permitted to spur off to one double socket in just 2.5mm T&E. We are not suggesting that 2.5mm will be ok at 32a.
Happy to be corrected so long as it's constructive.

I read what you wrote in post #19 to mean that if an appliance is only pulling 13A then it's ok to use a 2.5mm radial and protect it using a 32A breaker. If that is indeed what you meant then yes, your reply is incorrect, however I'm not so sure now that is what you meant.

Could you eleaborate for me so that I understand fully the solution you propose?
 
I read what you wrote in post #19 to mean that if an appliance is only pulling 13A then it's ok to use a 2.5mm radial and protect it using a 32A breaker. If that is indeed what you meant then yes, your reply is incorrect, however I'm not so sure now that is what you meant.

Could you eleaborate for me so that I understand fully the solution you propose?

OK, cool. I was just repying to IPU post #15 asking what would be protecting the 2.5 from the switch to the FCU. I think he was asking what was stopping the full 32a from going down that spur. The OP was designing a radial circuit with a 32a CB in 6mm and then suggesting drops from each switch to FCU in 2.5. I was telling IPU in my opinion this was ok as each drop was a single spur off the radial via a DP switch. The radial itself would need to be =>4mm on 32a but a single spur to a FCU would not.
 
Ah, ok, well, yes, unfortunately, in my opinion, you are incorrect as there is no such thing as a spur on a radial circuit. The breaker has to be selected so that it protects all cables within the circuit.

If you have a 32A breaker and 4mm feeding the grid switch, you would need 4mm feeding each 13A SFCU also. Only from the SFCU to the appliance could you then use 2.5mm cable.

Lets say for example you wanted to take a feed off a 40A cooker circuit to feed a single socket outlet (not that anyone would do it this way) then you wouldn't be able to take a 2.5mm feed from the cooker outlet plate to a SFCU, then on to the socket. The feed to the SFCU would have to be 6mm, the same as the cooker circuit. If you took a 2.5mm feed from the cooker outlet plate to a SFCU, even if it was only a few inches, then that length of cable between the cooker outlet plate and the SFCU would not be adequately protected.

My solution to the OP's problem seems the simplest:

Use two seperate A3 radial circuits, each supplying half of the 20A DP switches within the grid, then use 2.5mm cable straight from each individual grid switch to each individual socket outlet designed to supply an appliance. There is also no need for SFCU's whatsoever.

I myself have done this a couple of times but only using one A3 radial to supply the grid switches as there was only 4/5 appliances in each scenario.
 

Reply to Kitchen Appliance circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Great idea, thank you mate :)
2
Replies
38
Views
5K
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
380
If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...
Replies
1
Views
991

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks