To all you experienced fault finding electricians out there, any help appreciated on the below problem

A busy kitchen in a busy restaurant which is almost open 24/7 has a metal worktop. Kitchen staff occaisonally get minor shocks from worktop. Sockets in the vicinity are from 2 circuits. Both have been tested 1 is almost perfect. IR readings above 100 M.ohms
the other is a bit iffy (about 3.5 M.ohms from L/N to Earth.
Although low i dont deem this enough to present an immediate danger.

The shocks tend to happen whilst using portable kitchen appliances on the metal worktop. They have been tested all ok. I am guessing there is plenty of water splashing around but the staff are a bit low on detail which only adds to the problem

The worktop is not bonded but is earthed through other equipment as it is bolted to a series of other worktops & eventually to a splashback which has metal clad isolators & sockets fixed directly on it so i can only assume it is earthed through these. Hence i have 240v across worktop & live conductors of nearbye sockets.

Do I

A. remove all parrallel earth connections from the worktop. It is not an extraneaus item so is not required to be bonded
B. get to the bottom of the Low IR readings on the iffy circuit
C. Both
D. anything else?

I have been called to investigate this issue several times but never really get any headway as the kitchen is always so busy. I proposed spending a night in the restaurant without any kitchen staff in the way. But With Sunday night from midnight the only possibility for this restaurant the labour costs were too excessive for them. However very recently one member of staff recieved a serious shock which has prompted the restaurant management into action. So now i am under pressure to resolve it but it is difficult one & whatever option i choose its going to be expensive for them (Sunday night x 2 electricians) so i want to get it right

Thanks in advance for any idea's
 
If someone has received a shock then the restaurant owners should, assuming they actually give a flying something about their staff, be making an effort to get this resolved not paying lip service to it by telling you to work at ridiculous hours.
If this shock was reported they might find themselves closed by the powers that be until they prove that their installation is not making the environment unsafe to work in.
I'm sorry but this just beggars belief.
As the electrician responsible for putting this right I do not envy your position.
 
No They dont!
That was my first recomendation but they refused it as they didnt want any nuisance tripping!
I will insist on it now though. & was thinking of individual RCD sockets rather than rcbo to minimise the nuisance tripping
But still need to get to the bottom of the problem
 
It's pointless having rcd sockets in this setup in a way as its not going to reduce the risk if the worktop is live.

Are you sure it's not something as simple as nylon soled shoes then earthing through the worktop, getting a static shock... Just a thought.
 
if there is a dodgy fryer/fridge/mixer around with plenty of earth leakage then parts of worktop may get some voltage on them, and if not earthed properly... continuity test between worktops and db may help
 
These clowns need to be reminded that they have a legal responsibility to provide a workplace which is as safe as it possibly can be. If that means getting someone with a bit of clout in like Environmental Health or the HSE then so be it.
Would they be so blasé about it if a staff member were seriously hurt or killed?
 
I will almost definately be fitting RCD's to all sockets & whatever is required to improve the IR readings on the iffy circuit. The worktop issue is the bit i am unsure about should it be earthed or not? The regs say not but am i putting the staff in more danger if i remove all parallel earths?
 
I'd be looking to get everything I could with an electrical connection permanently off the tables. Then I'd test to see if the tables are an ECP. If they are I'd bond them, if not I wouldn't.
 

Reply to Kitchen nightmare in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
391

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top