To all you experienced fault finding electricians out there, any help appreciated on the below problem

A busy kitchen in a busy restaurant which is almost open 24/7 has a metal worktop. Kitchen staff occaisonally get minor shocks from worktop. Sockets in the vicinity are from 2 circuits. Both have been tested 1 is almost perfect. IR readings above 100 M.ohms
the other is a bit iffy (about 3.5 M.ohms from L/N to Earth.
Although low i dont deem this enough to present an immediate danger.

The shocks tend to happen whilst using portable kitchen appliances on the metal worktop. They have been tested all ok. I am guessing there is plenty of water splashing around but the staff are a bit low on detail which only adds to the problem

The worktop is not bonded but is earthed through other equipment as it is bolted to a series of other worktops & eventually to a splashback which has metal clad isolators & sockets fixed directly on it so i can only assume it is earthed through these. Hence i have 240v across worktop & live conductors of nearbye sockets.

Do I

A. remove all parrallel earth connections from the worktop. It is not an extraneaus item so is not required to be bonded
B. get to the bottom of the Low IR readings on the iffy circuit
C. Both
D. anything else?

I have been called to investigate this issue several times but never really get any headway as the kitchen is always so busy. I proposed spending a night in the restaurant without any kitchen staff in the way. But With Sunday night from midnight the only possibility for this restaurant the labour costs were too excessive for them. However very recently one member of staff recieved a serious shock which has prompted the restaurant management into action. So now i am under pressure to resolve it but it is difficult one & whatever option i choose its going to be expensive for them (Sunday night x 2 electricians) so i want to get it right

Thanks in advance for any idea's
 
Thanks Trevor, I knew what it was but was just trying to think of the words, it's been a long day, been out since 8am, got in at 7, been in a sodding loft all day fiddling about with lights etc, and whilst at it some loft people were boarding the loft cutting wood and stirring up all the nasty yellow fibreglass, the shower was much welcomed tonight!
 
Off the subject, on the way home I had a little job to do, fit a light in a bathroom, I mentioned it the other day but can't remover which thread, joist of it is, the old boy, his mrs died of cancer and his pull cord in the bathroom reminded him of her getting up in the night with the noise, any way, I couldn't put a switch on the outside as no rcd for new length of cable in wall.

I took his flying saucer heater thing off the ceiling tonight, replaced it with a 2D fitting and stuck a flush mounted pir next to it with the pull cord cut short near the ceiling as an over ride for the pir, looked great, bloke was well impressed, no rcd, but like for like swap execluding 6" of three core to pir.

He can now forget about his dead wife.
 
It's pointless having rcd sockets in this setup in a way as its not going to reduce the risk if the worktop is live.

Are you sure it's not something as simple as nylon soled shoes then earthing through the worktop, getting a static shock... Just a thought.

Up until now the general thoughts were that it could be something as minor as this but the recent more serious incident has changed those perceptions
 
his mrs died of cancer and his pull cord in the bathroom reminded him of her getting up in the night with the noise, He can now forget about his dead wife.
I remember that one, it seemed a really really bizarre thing to remind someone of a dead loved one. It affects everyone a different way though.
 
I remember that one, it seemed a really really bizarre thing to remind someone of a dead loved one. It affects everyone a different way though.

He only wanted a light switch moving but was a little more involved and long winded really, but he is pleased with the final product, he can now go in his bathroom and the light just comes on! You should have seen his face light up, it was nice to see. The poor sod himself has had it bad, has had 5 brain hemp rages and has 4 shunts in his head! I shouldn't really complain about working in a loft when you hear things like that.
 

Reply to Kitchen nightmare in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
391

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top