Hi guys,

Customer woke up this morning with the Main switch/RCD tripped. He narrowed the problem down to the kitcken ring so He unplugged all the counter top appliances and switched all the big under counter appliances off at the switches.

I got there and turned the mcb on then plugged the toaster in first and the RCD tripped. I then punplugged the toaster and reset the RCD. I then plugged everything in the kitchen in One by one and left each appliance plugged in individually for 5 - 10 mins each, the only thing that that tripped the RCD was when I plugged the freezer in.

I checked the wiring behind each socket and all was ok. So I plugged everything in except for the freezer and the RCD didnt trip. I waited for nearly an hour and no trip even with the toaster plugged in and the switch turned on.

I didnt have any test equipment on me but I`m going back tmrw with test equipment, so my question is can anybody advise on possibley the quickest way to iddentify the cause of the fault?

Thanks
 
agree with tel,otherwise the diy sheds could not sell any electrical accessories as the diy bloke couldnt change a socket without having to call someone out to test and inspect/issue a mwc.

Get your point however they still sell Consumer Units to anyone. See a fully loaded G.E one for ÂŁ50 in there the other week.
Surely a board change is not considered like for like is it?
 
Last edited by a moderator:
Get your point however they still sell Consumer Units to anyone. See a fully loaded G.E one for ÂŁ50 in there the other week.
Surely a board change is not considered like for like is it?

Could be I suppose, if the configuration and protective devices are all identical to the existing...ie a replacement due to damage to the existing....a CU upgrade would not be like for like though.
 
Thanks to most of you guys for all your responses apart from the odd 1 or 2 of you. If you got nothing helpful to say, I`d rather you not comment on my threads.


I was back on the job today with my tester, I done ring end to end continuity 0.51 L-L 0.52 N-N 0.84 E-E. IR test, lowest reading i got was 250M Ohm.


Everything in the house stays on, under load aswell untill I plug the freezer in and.....boom RCD trips within 30secs. So my conclusion is the freezer is the problem ( its a smeg under counter job if that helps ) Ive never claimed to be an 20 - 40 year experienced spark, thats why I am on this forum which I find a great source of info from lots of experienced sparks.

Im new to testing and fault finding so am I missing something Guys?
 
most probably be the freezer pal, as said above if all IR test is clear l-e, n-e, then circuit is fine,
just to prove you have found the fault a PAT on the applience would show leakage to earth,
 
most probably be the freezer pal, as said above if all IR test is clear l-e, n-e, then circuit is fine,
just to prove you have found the fault a PAT on the applience would show leakage to earth,

Thanks chopper, never done PAT and aint got the equipment. Any tests I could do with my multifunction tester on the appliance mate. Its my mates house and dont want him to have to call out a PAT man and part with his cash.

Thanks
 
Hi mate,

you could join L-N of the appliance and IR test @ 500v (test @ 250V first) to earth/metalwork of the appliance, it would be better if the appliance was disconnected from the fixed wiring for this, as this is all a PAT test would do with regards to the IR test part. and see what you get.
 
Hi mate,

you could join L-N of the appliance and IR test @ 500v (test @ 250V first) to earth/metalwork of the appliance, it would be better if the appliance was disconnected from the fixed wiring for this, as this is all a PAT test would do with regards to the IR test part. and see what you get.

cheers mate, do you think that anything under 2M Ohm could be suspect as is usually the case?
 
under 2M Ohm could be suspect as is usually the case?

I would expect anything less than 1 Meg for class 1 to be suspect, others may wish to correct me if Iam wrong.

This method does not replace a PAT test per se, but will show up faulty equipment.

Ps. if the appliance is faulty, I would expect your IR result to be a lot lower than 1 Meg, as a 30mA RCD will trip with a combined 'leakage resistance to earth' anywhere from about 8K ohms to about 15K ohms, depending on the actual RCD tripping current checked on the Ramp test
 
Last edited:
the other thing to note is the MWC itself asks for "details of the modified circuit". replacing a fitting /accessory is not modifying the circuit. therefore, IMO, no certificate is required (although i do not dispute the idea that it may be advantageous to complete a test of the circuit and issue a MW

edit:sorry, double post.

Hi Tel.

Just looking at the MWC in the BRB (page 335). Could you clarify where it refers to 'details of modified circuit' in the certificate?
 
Thanks to most of you guys for all your responses apart from the odd 1 or 2 of you. If you got nothing helpful to say, I`d rather you not comment on my threads.


I was back on the job today with my tester, I done ring end to end continuity 0.51 L-L 0.52 N-N 0.84 E-E. IR test, lowest reading i got was 250M Ohm.


Everything in the house stays on, under load aswell untill I plug the freezer in and.....boom RCD trips within 30secs. So my conclusion is the freezer is the problem ( its a smeg under counter job if that helps ) Ive never claimed to be an 20 - 40 year experienced spark, thats why I am on this forum which I find a great source of info from lots of experienced sparks.

Im new to testing and fault finding so am I missing something Guys?

I stand vindicated!

As to are you missing something, it’s just experience which will come with time.
 
Last edited by a moderator:

Reply to Kitchen Ring earth fault? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
969
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
425
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top