Yep one socket spur from a ring main is OK as the 2.5mm cable can handle that, but there is a rule that the spur cannot be more than 1/8th the length of the ring but you also have to consider that the cable can dissipate its heat wherever it is run.
As with everything this is to do with safety, I will explain something that I think sparkys learn in the first year at college as it does not sound like you have done any cable calcs:
A 2gang 13A socket could draw 26A down the spur cable - so if you run 8 double sockets (I can't remember if you said 8 doubles or 8 total) that's a max potential of 8accesories x2socketsx13A in the plug fuses = 512A so you will blow your circuit protective device (the MCB etc in the Consumer Unit), however the real problem would come if you run the 8 double sockets with say just 3 amps each = 8x2x3A = 48Amps which is far more than your 2.5 can handle and will make it catch fire and your house and you in bed! now you will say the circuit protective device is a 32A so it will go right? But in a domestic dwelling you will expect a type b protective device typically, that could happily sit there with 48A amps for a while as a type B device has a 3-5x tripping characteristic which means to make it blow nice and fast you could in the worst case scenario need 32Ax5 = 160A... so yes your house could burn down if you install 8 double sockets so get a sparky in...