Hi everyone

I am tearing my hair out here. I have trying to get UK Power Networks to quote for new electrical supplies in a property development I am managing. The property is a conversion into four one bed flats.

I have been asked by UKPN to provide the After Diversity Max Demand in kVA for each unit. I have asked an electrician and he said 20kVA. I asked another and he said 24 kVA.

But UKPN said this:

"UK Power Networks would in general expect the (ADMD - after diversity maximum demand) for a gas heated flat/house to be between 1.5kVA and 3.0kVA and an electric heated flat/house to be between 5kVA & 10kVA unless abnormal high usage appliances are being installed."

These units will have electric wall heaters and will be very well insulated.
They will also each have 125l unvented cylinders for water heating. They will each have an oven/grill and washing machine.

I have asked UKPN how they arrived at this figure and they pointed me to their web site (which only confuses matters and fails to show how this is calculated):

UK Power Networks - What are Watts (W), Kilowatts (kW) and Kilovolt Amps (kVA)? - https://www.ukpowernetworks.co.uk/internet/en/help-and-advice/need-help/what-are-watts.html

But on their site it says this:

" If you’re unsure and don’t tell us what you need then we would assume 15kVA but it’s important you get this right. "

I cannot seem to get them to explain. Either they are clueless or I am clueless or both.

Can anyone help?

thanks
Gus
 
As has been stated before you will not have all appliances running at full load at the same time.

Once the heaters and oven are up to temperature they start cycling and the load drops right off.

Sockets and lighting I would expect to see no mare than 9 amps for an average 4 bed house. Yes this will spike when the kettle goes on etc but this is for a very short duration.

On a rough calculation you could more than likely get away with a 15kVA per flat.

However what sort of client are you aiming for? Young single professionals would have different usage and timings than a family with four kids...
 
Thanks Strima, that's very helpful. As UKPN networks stated they suggest 5-10vVA ADMD for an electrically heated home. However, they are unable to tell me how they arrived at this estimation.

The four flats will be almost certainly be rented to young professionals. They will be out all day during the week but will likely have very similar energy usage patterns. i.e. They will want the heating on for a spell in the morning and evening. They will all be home around the same time and likely to put the oven on.

During the summer this will not be an issue at all. I just want to be covered for hard, cold spells during the winter.

However, I am coming around to the idea that 17.25kVA should be enough per flat. I just want to make sure I make the right decision now as getting it wrong now could be a nightmare later.
 
UKPN came back to me and said they could supply 23kVA by routing from another source without additional cost so am going with that.
I got a quote from them and ma now looking to find someone to do the contestable stuff. UKPN are very slow and the quote seems a lot.

Can anyone recommend a contractor that can do this kind of stuff in South London?
thanks
 
UKPN came back to me and said they could supply 23kVA by routing from another source without additional cost so am going with that.
I got a quote from them and ma now looking to find someone to do the contestable stuff. UKPN are very slow and the quote seems a lot.

Can anyone recommend a contractor that can do this kind of stuff in South London?
thanks

Hi Gus,

This thread has been very interesting. I am in a similar situation. I have a large house that is being converted to 4 x 1 bed flats for young professionals plus a landlord supply. That means 4 x dishwasher, washer/dryer, induction hob, electric oven etc. I also want the landlord supply to be enough to allow for an electric car charge point in the future. I also want to plan for the fact it's looking like gas boilers will be phased out in favor of electric within 10-15 years.

My spark came back and said each flat would have an 80Amp (AD) demand based on appliances and that 100Amp would be ideal given lighting, plugs etc So 23Kva.

5 x 23Kva = 115KVa

My next question is that Ryefield boards are designed to sit on a 100Amp supply (at least the ones I've looked at). A 115KVa supply would exceed this, no?

UK Power really need to do a dummys guide 101 on this.

Asking as a property owner/non-spark.
 
Hi Gus,

This thread has been very interesting. I am in a similar situation. I have a large house that is being converted to 4 x 1 bed flats for young professionals plus a landlord supply. That means 4 x dishwasher, washer/dryer, induction hob, electric oven etc. I also want the landlord supply to be enough to allow for an electric car charge point in the future. I also want to plan for the fact it's looking like gas boilers will be phased out in favor of electric within 10-15 years.

My spark came back and said each flat would have an 80Amp (AD) demand based on appliances and that 100Amp would be ideal given lighting, plugs etc So 23Kva.

5 x 23Kva = 115KVa

My next question is that Ryefield boards are designed to sit on a 100Amp supply (at least the ones I've looked at). A 115KVa supply would exceed this, no?

UK Power really need to do a dummys guide 101 on this.

Asking as a property owner/non-spark.

Off the top of my head that seems like a very high demand for each flat.

Ryfield boards are normally designed to be supplied at a bit more than 100A, they usually have 100A rated outgoing ways.

Nobody is going to produce a dummies guide because it is a technical subject and involves well established scientific principles and calculations, without learning this and gaining experience working alongside those who are experienced at it you can't get it right.
There are too many variables and considerations to reduce it down to a simplified guide.
 

Reply to kva for a flat with all electric heating in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
782
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
492
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top