Trainee here so it's likely I've got my wires crossed!

I've got a small unoccupied rental property which had a rewirable fuseboard which my work colleague (fully qualified spark) and I replaced the other day with an 8 way RCBO board, surge protected. He did the board change while I replaced some sockets with USB charging sockets.

Initial end to end testing on the Ring Final indicated that there was a break in the ring somewhere, so we swapped out the 32a breaker for a 20a. All circuits were holding fine on the RCBO's after we went home on Friday evening. The plan was that I would come back today to investigate the broken ring, carry out some testing and to label up the board.

So, when I got back to the property today I plugged my socket tester into a socket and it indicated Live Earth Reversal. I pulled off all the sockets to check they were all wired correctly and they all looked good. Using my MFT I tested the voltage between L-N and it showed 60v, between N-E voltage was 190.

Any ideas?
 
Trainee here so it's likely I've got my wires crossed!

I've got a small unoccupied rental property which had a rewirable fuseboard which my work colleague (fully qualified spark) and I replaced the other day with an 8 way RCBO board, surge protected. He did the board change while I replaced some sockets with USB charging sockets.

Initial end to end testing on the Ring Final indicated that there was a break in the ring somewhere, so we swapped out the 32a breaker for a 20a. All circuits were holding fine on the RCBO's after we went home on Friday evening. The plan was that I would come back today to investigate the broken ring, carry out some testing and to label up the board.

So, when I got back to the property today I plugged my socket tester into a socket and it indicated Live Earth Reversal. I pulled off all the sockets to check they were all wired correctly and they all looked good. Using my MFT I tested the voltage between L-N and it showed 60v, between N-E voltage was 190.

Any ideas?
Done any r1 r2 testing?
 
Done any r1 r2 testing?
Not yet. Was called home to other duties before I could get stuck in!
[automerge]1582477287[/automerge]
Sounds like a neutral problem...and if you've a break in the ring, where's the place to start?
What are the ring continuities?
I've been right through the property all sockets off and terminals checked. I found one that was pumped full of silicone but I replaced that one with a new socket and the fault remained.

Also, all sockets worked until we changed the board. The previous tenant had damaged a few sockets and had removed one, but I think I've accounted for all of that.
 
Last edited:
socket testers will often show L-E reversal if you have a floating N. that's where the fault is. a poor connection somewhere on N. do a end-end on N and then track it down by splitting the ring.
 
L-N and it showed 60v, between N-E voltage was 190.
If the voltages are stable with socket tester present ,
and they add to aprox 250 .
Something is floating up , due to presence of socket tester.
One of your notional ref points is actually a mid point voltage !
Think potential divider.

(2nd half of post self supressed -involved wagos ,a socket and fly cables --stay safe )
 
Last edited:
Had the exact same last week, broken neutral and disconnected CPC.
[ElectriciansForums.net] L-E reversed and low voltage on RFC
 
Thanks all for your help, it's much appreciated!

I've been back to the property this evening and tested the circuit.
  • End to ends were 0.64 (r1) and 1.11 (r2).
  • L-N tests at sockets ranged between 0.30 and 0.36.
  • L-CPC ranged between 0.39 and 0.48
  • Zs 0.66
When I screwed the conductors back in to their terminals in the CU the original fault rectified itself. I suspect there might have been a loose connection at the Neutral terminal?
 
OK, so you found a disconnect or a likely disconnect in the neutral, which was also indicated by your odd L-N and N-E voltages (both readings involving the neutral were wrong but the L-E voltage presumably OK). However, the socket tester reported a different kind of problem than the actual one present, which was confusing. L-E reversal is clearly very dangerous and in practice rather unlikely, so the first thing to think about in that situation is 'what is the test actually trying to tell me'. Socket testers are not very intelligent!

BTW, please always give the units when stating measurements:
L-N tests at sockets ranged between 0.30 and 0.36

If those numbers are ohms, I would make one diagnosis. If they are megohms, I would make another. Put a different way, would you be worried if I dropped something on your head that weighed 0.36?
 
OK, so you found a disconnect or a likely disconnect in the neutral, which was also indicated by your odd L-N and N-E voltages (both readings involving the neutral were wrong but the L-E voltage presumably OK). However, the socket tester reported a different kind of problem than the actual one present, which was confusing. L-E reversal is clearly very dangerous and in practice rather unlikely, so the first thing to think about in that situation is 'what is the test actually trying to tell me'. Socket testers are not very intelligent!

BTW, please always give the units when stating measurements:


If those numbers are ohms, I would make one diagnosis. If they are megohms, I would make another. Put a different way, would you be worried if I dropped something on your head that weighed 0.36?
Right on Lucien!
 

Reply to L-E reversed and low voltage on RFC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
378

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top