When you do a L&N-E IR test, is there anything (other than a fault) that could be left plugged in that would produce a low reading?
 
surge protection?
I'm not asking for a particular scenario, like I'm not having issues. Just wondering if there's any predicament that could cause a L&N-E IR test to cause a low reading and stick that knowledge in the back of my head somewhere.

I guess with surge protection, it would show on a 500V test but wouldn't show (or show to the same degree) on a 250V test?

Anything else?
 
IT equipment. computers are renown for having small earth leakage.typically around 3mA apiece. that's why you never put too many on a circuit with RCD protection.
 
IT equipment. computers are renown for having small earth leakage.typically around 3mA apiece. that's why you never put too many on a circuit with RCD protection.

See what I'm trying to understand is that the regs says it's okay to tie L&N together and test to earth when vulnerable equipment is on the circuit - so what would be the point of that if they give false results
 
I had a socket outlet RCD in a RFC give me low readings. Likewise a shaver point.
 
Well no, it's not necessarily a way of cutting corners. The regs describe the test, but my question is what benefit does it bring if the results are still going to be influenced by equipment
 
OK, the scenario where I'd imagine using this is not for an EIC but maybe to do a quick global IR to make sure an RCD will hold - obviously this will then have a full test but I'm thinking just a quick way to find out if it should generally be OK
 
Because the results are most likely going to be worse than if you split test with all loads disconnected. Thus if it passes with results that are going to be pulled down by equipment it stands to reason that the circuit is serviceable and without loads, be in better standing.
 
Its a handy method for EICRs when you either cant disconnect everything, or are unsure of any loads that are connected without your knowledge.
 

Reply to L&N-E IR Test (and we still haven't fixed the stupid 20 characters) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
354
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
603
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top