I really hope you not just going to guess at this.
I presume you have been ask to design an L2 fire alarm system, which apart from have an area within an area is designed as an L1 system, every area must have protection.
1. You need to evalauate the areas of each room and circulation areas for protection
2. evaluate db levels for sounders to achieve +65 db in all areas ( if hotel +75db in bedrooms)
3. Calculate loop designs for loop current and battery requirements (max 500mA per loop, 24hr standby and 30 mins alarm)
4. CAD and design the system then sumit to building control or main contractor for approval.
5. First fix the system (cable it)
6. 2nd fix the system (fix detection/sounders)
7. Write the program and upload (with caurse and effects requested)
8. Test and commission the whole system (operation of detection db levels in all areas)
9. Sumit full O&M manuals (cad drawings, zone charts, cable test sheets, db levels, loop battery calcs, caurse & effects and full programme data.
Hope you find time to read this brief listing of fire alarm design and installtion.